Built-up Sections:
Built-up sections are used as compression members for heavy loads and consist of one or more solid rolled steel section with flanges having cover plates. The cover plates are connected to the flanges by rivets or welds. These connections are designed to resist a shear force, which is 2.5% of the maximum compressive load on the column.
Example
Figure shows an ISHB 350 @ 72.4 kg/m with two flange plates 400 × 10 mm section each. Find out the load carrying capacity of the column if the effective length is 4.5 m (fy = 250 MPa).
Figure
Solution
Area of the ISHB section = 92.21 cm2
Ixx = 19802.8 cm4
Iyy = 2510.5 cm4
The minimum radius of gyration will be about the minor y-y axis.
Iyy of compound section = 25,105,000 + 2 ×(10 × 4003)/12
= 131, 771, 667 mm4
Area of compound section = 9221 + 2 × 400 × 10 = 17221 mm2
∴ rmin = = 87.5 mm
∴ λ = 4500/87.5 = 51.4
Corresponding allowable σac = 130.6 MPa (from Table 2)
∴ Load carrying capacity = σac . A = 130.6 × 17221 N = 2249 kN.