Test Schedule - Meter Testing
The test schedule as per the Central Electricity Authority Regulations on Installation and Operation of Meters is given below.
Table: Test Schedule
Meter Type
Schedule
Single Phase LT meters
Once in 5 years after installation
LT three phase meters (CT operated) 20 kVA to 100 kVA
Once in a year to be checked since these are installed for high value consumers
Other LT metering systems
Once in two years after installation
EHT / HT meters
The testing schedule for HT consumers should cover the whole Metering System involving CTs, PTs and Pilot Wire. Detailed ratio testing of CT, PT and control Pilot/ wires is to be completed. Testing by mobile vans/mobile cubicles through secondary injections kit and phantom loading might also be carried out through Measurement Unit. All new meters should meet the needs of Accuracy Class spelt out in Table.
Table: Requirements of Accuracy Class
Type of Consumer
Overall Accuracy Class
EHT Consumers (33 kV)
0.2
HT Consumer (44 to 33 kV)
0.5 or better
LT Consumer (Whole Current meters)
1.0 or better
LT Consumers (CT operated)
Q. Describe about digital communication systems fl A digital signal can be deflned as having any one of a finite number of discrete amplitudes at any given time. The signal coul
Q. For a BJT with vBE = 0.7V, I CBO = 4 nA, i E = 1 mA, and i C = 0.9 mA, evaluate α, iB,iSE, and β.
Q. Antinoise Systems — Noise Cancellation? Traditionally sound-absorbing materials have been used quite effectively to reduce noise levels in aircraft, amphitheaters, and other
Q. Explain Modulation and sampling? Modulation is the process whereby the amplitude (or another characteristic) of a wave is varied as a function of the instantaneous value of
truth table of decimal to seven segment
Apparatus for BCD to excess 3 convertor using nand and nor gates
Q. Explain Television signal transmission? Television signals in television signal transmission are the electric signals generated by converting visual images through raster (T
Successive approximation ADC One method of addressing digital ramp ADC's shortcomings is so-called successive approximation ADC. Only change in this design is a very special c
Mode1 When the positive pulse from PWM is applied to the transistor Q shown in figure it gets turned on. In this condition current flows through transistor Q and.
Methods of Testing Irrespective of reasons, testing is commonly carried out 1. On site, or 2. In a Meter Testing Station (MTS) accredited as per IS/ISO/IEC 17025.
Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!
whatsapp: +1-415-670-9521
Phone: +1-415-670-9521
Email: [email protected]
All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd