Test Schedule - Meter Testing

The test schedule as per the Central Electricity Authority Regulations on Installation and Operation of Meters is given below.

Table: Test Schedule

Meter Type

Schedule

Single Phase LT meters

Once in 5 years after installation

LT three phase meters (CT operated) 20 kVA to 100 kVA

Once in a year to be checked since these are installed for high value consumers

Other LT metering systems

Once in two years after installation

EHT / HT meters

Below 5 MVA - Once in a year
5 to 10 MVA - Once in six months
above 10 MVA - Once in a quarter

The testing schedule for HT consumers should cover the whole Metering System involving CTs, PTs and Pilot Wire. Detailed ratio testing of CT, PT and control Pilot/ wires is to be completed. Testing by mobile vans/mobile cubicles through secondary injections kit and phantom loading might also be carried out through Measurement Unit. All new meters should meet the needs of Accuracy Class spelt out in Table.

                                                   Table: Requirements of Accuracy Class

Type of Consumer

Overall Accuracy Class

EHT Consumers (33 kV)

0.2

HT Consumer (44 to 33 kV)

0.5 or better

LT Consumer (Whole Current meters)

1.0 or better

LT Consumers (CT operated)

1.0 or better

 


Related Discussions:- Test schedule - meter testing

Potentiometers , Which potentiometer do I need to control; 6v 2amps dc?

Which potentiometer do I need to control; 6v 2amps dc?

Properties and application of permanent magnetic materials, Give the proper...

Give the properties and application of permanent magnetic materials. Permanent magnetic materials: Properties: Permanent magnetic materials have a huge area of hyster

Deviations from purchasing power parity, Q. Does the existence of non-trada...

Q. Does the existence of non-tradable goods allow for deviations from Purchasing Power Parity? Answer: Yes the continuation of non-tradable goods permits deviations from Purch

truth table in sop form, Normal 0 false false false EN...

Normal 0 false false false EN-IN X-NONE X-NONE MicrosoftInternetExplorer4

Symmetrical fluctuating message, A symmetrical fluctuating message, with |f...

A symmetrical fluctuating message, with |f(t)| max = 6.3 V and KCR = 3, is to be encoded by using an encoder that employs an 8-bit natural binary code to encode 256 voltage levels

Transistor in the common base configuration, Draw the circuit of transistor...

Draw the circuit of transistor in the common base configuration. Draw the Active, saturation and cut-off region. List the characteristics of Ideal Op-Amp. Sketch the pin diagram

Specific core indicators method, Specific Core Indicators Method This ...

Specific Core Indicators Method This technique emphasizes to assign the responsibility and create the accountability. It is possible in which for any of the main indicators, t

Jfet ampli?er circuit, Q. For the CS JFET ampli?er circuit of Figure, R D ...

Q. For the CS JFET ampli?er circuit of Figure, R D = 2k and R L = 3k. The JFET with ro = 15 k has a voltage gain A v1 =-4.5 when the entire source resistance is bypassed. Fin

How transistor will be used as an amplifier, (a) How transistor will be use...

(a) How transistor will be used as an amplifier? (b) Give relation between α and β? (c) Show the biasing arrangement for the PNP transistor in common base configuration, so t

Why two rectifier is used in smps, Its not essential that a power plant use...

Its not essential that a power plant uses only two rectifiers, it depends on the load there at the site and the capacity of the rectifier or SMPS. Assume the load at the site is 12

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd