Starting methods for polyphase induction motors, Electrical Engineering

Assignment Help:

Starting Methods for Polyphase Induction Motors

When high starting torques are required, a wound-rotor induction motor, with external resistances inserted in its rotor circuits, can be used. The starting current can be reduced and high values of starting torque per ampere of starting current can be obtained with rotor-resistance starting. The external resistances are generally cut out in steps as the machine runs up to speed.

For squirrel-cage-rotor machines, the problem is to keep down the starting current while maintaining adequate starting torque. The input current, for example, can be no more than 6 times the full-load current,while the starting torquemay be about 1.5 times the full-load torque.Depending on the capacity of the available supply system, direct-on-line starting may be suitable only for relatively small machines, up to 10-hp rating. Other starting methods include reduced-voltage starting by means of wye-delta starting, autotransformer starting, or stator-impedance starting.

883_Starting Methods for Polyphase Induction Motors.png

For employing the wye-delta starting method, a machine designed for delta operation is connected in wye during the starting period. Because the impedance between line terminals for wye connection is three times that for delta connection for the same line voltage, the line current at standstill for wye connection is reduced to one-third of the value for delta connection. Since the phase voltage is reduced by a factor of √3 during starting, it follows that the starting torque will be one-third of normal. For autotransformer starting, the setting of the autotransformer can be predetermined to limit the starting current to any desired value.An autotransformer,which reduces the voltage applied to the motor to x times the normal voltage, will reduce the starting current in the supply system as well as the starting torque of the motor to x2 times the normal values.

Stator-impedance starting may be employed if the starting-torque requirement is not severe. Series resistances (or impedances) are inserted in the lines to limit the starting current. These resistances are short-circuited out when the motor gains speed. This method has the obvious disadvantage of inefficiency caused by the extra losses in the external resistances.


Related Discussions:- Starting methods for polyphase induction motors

For the circuit obtain z- and y-parameters, Q. For the circuit shown in Fig...

Q. For the circuit shown in Figure, obtain: (a) z-and y-parameters; (b) Transfer function I 2 /I 1 when V 2 = 0.

Bode plot phase ad gain margin, Using Bode plot calculate (a) Phase margin ...

Using Bode plot calculate (a) Phase margin (b) Gain margin (c) Stability of closed loop system. The open transfer function of the system is t=30/(s+2)/(s+3)Using Bode plot calcula

Downsampling in dsp, #ques1. (MATLAB) Generate 100 samples of the signal ...

#ques1. (MATLAB) Generate 100 samples of the signal  = sin (0.125). We want to decimate this signal using D = 2. • Design a 25-order lowpass filter using the Parks-McClella

Metering standards, Metering Standards Relevant standards on metering ...

Metering Standards Relevant standards on metering are given in Table. Table: Relevant Metering Standards  Standards Description

Transistor, Various compensation techniques

Various compensation techniques

Write short note on quantization, Q. Write short note on Quantization? ...

Q. Write short note on Quantization? Quantization: This is first step in PCM. Total amplitude range of the modulating signal is divided into a number of standard levels calle

Mobile and wirelss communicatio, In a CDMA system, the signal is spr...

In a CDMA system, the signal is spread over a large bandwidth by multiplying the transmitted symbol by a sequence of short pulses, also called chips. The

Calculate the rated load current of machine, A 500 MVA, 33kv, three phase s...

A 500 MVA, 33kv, three phase steam turbine generator has a synchronous reactance of 1.6 p.u. It delivers a rated output at 0.8 power factor lagging. Calculate (a) The synchronou

Comparison of induction and dielectric heating , Comparison  of Induction ...

Comparison  of Induction and Dielectric Heating After  studying the induction and  dielectric  heating  followings  points  may consider for  comparison  between  induction an

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd