Starting methods for polyphase induction motors, Electrical Engineering

Assignment Help:

Starting Methods for Polyphase Induction Motors

When high starting torques are required, a wound-rotor induction motor, with external resistances inserted in its rotor circuits, can be used. The starting current can be reduced and high values of starting torque per ampere of starting current can be obtained with rotor-resistance starting. The external resistances are generally cut out in steps as the machine runs up to speed.

For squirrel-cage-rotor machines, the problem is to keep down the starting current while maintaining adequate starting torque. The input current, for example, can be no more than 6 times the full-load current,while the starting torquemay be about 1.5 times the full-load torque.Depending on the capacity of the available supply system, direct-on-line starting may be suitable only for relatively small machines, up to 10-hp rating. Other starting methods include reduced-voltage starting by means of wye-delta starting, autotransformer starting, or stator-impedance starting.

883_Starting Methods for Polyphase Induction Motors.png

For employing the wye-delta starting method, a machine designed for delta operation is connected in wye during the starting period. Because the impedance between line terminals for wye connection is three times that for delta connection for the same line voltage, the line current at standstill for wye connection is reduced to one-third of the value for delta connection. Since the phase voltage is reduced by a factor of √3 during starting, it follows that the starting torque will be one-third of normal. For autotransformer starting, the setting of the autotransformer can be predetermined to limit the starting current to any desired value.An autotransformer,which reduces the voltage applied to the motor to x times the normal voltage, will reduce the starting current in the supply system as well as the starting torque of the motor to x2 times the normal values.

Stator-impedance starting may be employed if the starting-torque requirement is not severe. Series resistances (or impedances) are inserted in the lines to limit the starting current. These resistances are short-circuited out when the motor gains speed. This method has the obvious disadvantage of inefficiency caused by the extra losses in the external resistances.


Related Discussions:- Starting methods for polyphase induction motors

Data analysis in gis, Data analysis in GIS: Therefore, GIS consists of...

Data analysis in GIS: Therefore, GIS consists of the following: 1.  Database - for storage and retrieval of information. The database forms the foundation of the GIS syst

Determine the total energy ?owing into the component, Q. The voltage at ter...

Q. The voltage at terminal a relative to terminal b of an electric component is v(t) = 20 cos 120πt V. A current i(t) =-4 sin 120πt A ?ows into terminal a. From time t 1 to t 2 ,

Magnetic permeability and the definition of the amp, The ampere has been de...

The ampere has been defined (by the International Committee of Weights and Measures in 1946) as the current flowing in two long parallel wires 1 metre apart that produces a force o

Illustrate hexadecimal number system, Q. Illustrate Hexadecimal Number Syst...

Q. Illustrate Hexadecimal Number System? A big difficulty with the binary system is verbosity. To symbolize the value 202 requires eight binary digits. The decimal version n

Sketch the waveforms of sinusoidal voltage source, Q. Consider the op-amp c...

Q. Consider the op-amp circuit of Figure. Sketch the waveforms of v S and v o , if v S is a sinusoidal voltage source with a peak value of 2.

Linear system to a unit-step excitation, Q. The response v(t) of a linear s...

Q. The response v(t) of a linear system to a unit-step excitation i(t) is given by v(t) = (5 - 3e -t + 2e -2t ) u(t). Determine the transfer function H(s) = V (s)/I (s).

Illustrate inductance with example, Q. Illustrate Inductance with example? ...

Q. Illustrate Inductance with example? An ideal inductor is also an energy-storage circuit element (with no loss associated with it) like a capacitor, but representing the magn

Find the percent voltage regulation of the transformer, Q. A 25-kVA, 2400/2...

Q. A 25-kVA, 2400/240-V, 60-Hz, single-phase transformer has an equivalent series impedance of 3.45 + j5.75  referred to the primary high voltage side. The core loss is 120 W. Whe

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd