Starting methods for polyphase induction motors, Electrical Engineering

Assignment Help:

Starting Methods for Polyphase Induction Motors

When high starting torques are required, a wound-rotor induction motor, with external resistances inserted in its rotor circuits, can be used. The starting current can be reduced and high values of starting torque per ampere of starting current can be obtained with rotor-resistance starting. The external resistances are generally cut out in steps as the machine runs up to speed.

For squirrel-cage-rotor machines, the problem is to keep down the starting current while maintaining adequate starting torque. The input current, for example, can be no more than 6 times the full-load current,while the starting torquemay be about 1.5 times the full-load torque.Depending on the capacity of the available supply system, direct-on-line starting may be suitable only for relatively small machines, up to 10-hp rating. Other starting methods include reduced-voltage starting by means of wye-delta starting, autotransformer starting, or stator-impedance starting.

883_Starting Methods for Polyphase Induction Motors.png

For employing the wye-delta starting method, a machine designed for delta operation is connected in wye during the starting period. Because the impedance between line terminals for wye connection is three times that for delta connection for the same line voltage, the line current at standstill for wye connection is reduced to one-third of the value for delta connection. Since the phase voltage is reduced by a factor of √3 during starting, it follows that the starting torque will be one-third of normal. For autotransformer starting, the setting of the autotransformer can be predetermined to limit the starting current to any desired value.An autotransformer,which reduces the voltage applied to the motor to x times the normal voltage, will reduce the starting current in the supply system as well as the starting torque of the motor to x2 times the normal values.

Stator-impedance starting may be employed if the starting-torque requirement is not severe. Series resistances (or impedances) are inserted in the lines to limit the starting current. These resistances are short-circuited out when the motor gains speed. This method has the obvious disadvantage of inefficiency caused by the extra losses in the external resistances.


Related Discussions:- Starting methods for polyphase induction motors

Transformers, Three transformers are provided with the following rating val...

Three transformers are provided with the following rating values: 1) 2400/240 V, 55kVA, Req1 = (0.1 + 0.0Y) Ohm and Xeq1 = (0.15 + 0.XX) Ohm. 2) 240/120 V, 25kVA, Req1 = (0.1

Use delta-wye transformation for network reduction, Use delta-wye transform...

Use delta-wye transformation for network reduction and determine the current through the 12- resistor in the circuit of Figure(a).

Plagiarised Content, Your site is full of plagiarised content even though y...

Your site is full of plagiarised content even though you claim to be and I quote "Plagiarism Free". You should not be charging for this content, the site and service is a fraud.

Explain noise, Explain Noise Noise is unwanted signals which degrade t...

Explain Noise Noise is unwanted signals which degrade the desired signal content and therefore the performance of the system. Noise might be produced either externally or inte

Power Engineering, A three-phase transposed line is composed of one ACSR co...

A three-phase transposed line is composed of one ACSR conductor per phase with flat horizontal spacing of 11 meters as shown in Figure (a). The conductors have a diameter of 3.625

Illustrate the experts model of GPS system, Illustrate the experts model of...

Illustrate the experts model of GPS System A fundamental expert system is made up of the below elements: Setting up an Expert System -  Information is collected

Show quantization process, Q. Show Quantization process Let Figure (a) ...

Q. Show Quantization process Let Figure (a) illustrate a message f (t) with values between 0 and 7 V. A sequence of exact samples taken at uniform intervals of time is shown: 1

Metering and billing system, Metering and Billing System Previously, y...

Metering and Billing System Previously, you have learnt about various measures for reducing commercial losses of a utility. You have studied in which the metering and billing

Find the thevenin equivalent, Task 1 Use basic circuit theory to...

Task 1 Use basic circuit theory to convert the "T" circuit below into the equivalent "π". Hint: Remember to disconnect the voltage source and the load. Task 2

Develop a block diagram for a two-port network, Q. The equations for a two-...

Q. The equations for a two-port network are given by V 1 = z 11 I 1 + z 12 I 2 0 = z 21 I 1 + (z 22 + Z L )I 2 V 2 = - I 2 Z L (a) Satisfying the equations, dev

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd