Starting Methods for Polyphase Induction Motors

When high starting torques are required, a wound-rotor induction motor, with external resistances inserted in its rotor circuits, can be used. The starting current can be reduced and high values of starting torque per ampere of starting current can be obtained with rotor-resistance starting. The external resistances are generally cut out in steps as the machine runs up to speed.

For squirrel-cage-rotor machines, the problem is to keep down the starting current while maintaining adequate starting torque. The input current, for example, can be no more than 6 times the full-load current,while the starting torquemay be about 1.5 times the full-load torque.Depending on the capacity of the available supply system, direct-on-line starting may be suitable only for relatively small machines, up to 10-hp rating. Other starting methods include reduced-voltage starting by means of wye-delta starting, autotransformer starting, or stator-impedance starting.

883_Starting Methods for Polyphase Induction Motors.png

For employing the wye-delta starting method, a machine designed for delta operation is connected in wye during the starting period. Because the impedance between line terminals for wye connection is three times that for delta connection for the same line voltage, the line current at standstill for wye connection is reduced to one-third of the value for delta connection. Since the phase voltage is reduced by a factor of √3 during starting, it follows that the starting torque will be one-third of normal. For autotransformer starting, the setting of the autotransformer can be predetermined to limit the starting current to any desired value.An autotransformer,which reduces the voltage applied to the motor to x times the normal voltage, will reduce the starting current in the supply system as well as the starting torque of the motor to x2 times the normal values.

Stator-impedance starting may be employed if the starting-torque requirement is not severe. Series resistances (or impedances) are inserted in the lines to limit the starting current. These resistances are short-circuited out when the motor gains speed. This method has the obvious disadvantage of inefficiency caused by the extra losses in the external resistances.


Related Discussions:- Starting methods for polyphase induction motors

Obtain an expression for b, Q. Consider an in?nitely long, straight wire (i...

Q. Consider an in?nitely long, straight wire (in free space) situated along the z-axis and carrying current of I A in the positive z-direction. Obtain an expression for ¯ B everywh

Draw and explain a monostable multivibrator, Q. Draw and explain a monostab...

Q. Draw and explain a monostable multivibrator ? The monostable configuration consists of two amplifier stages interconnected in such a manner as to possess one stable state. T

Sketch phasor diagrams for lagging power factor load, Q. For a transmission...

Q. For a transmission-line model that includes only the series impedance Z, sketch phasor diagrams for: (a) Lagging power factor load. (b) Leading power factor load.

Determine maximum length for cable, You have been asked to help on the desi...

You have been asked to help on the design of CDU's new electric vehicle. The vehicle is to be powered by a 96V, 300A battery pack and you need to decide on the maximum length you c

Decimal to binary coded decimal conversions, Decimal to Binary Coded Decima...

Decimal to Binary Coded Decimal Conversions Step1. Separate the digits in the decimal number Step2. Express each of the digits in their binary equivalent Step3. Combine all o

Induction motor, A 100hp,460v,8pole,60hz,star connected 3phase IM runs at 8...

A 100hp,460v,8pole,60hz,star connected 3phase IM runs at 891rpm under full load what is the speed of the rotor field relative to i)rotor structure ii)stator rotating field

Evaluate hysteresis loss, Q. A magnetic circuit is found to have an ac hyst...

Q. A magnetic circuit is found to have an ac hysteresis loss of 10 W when the peak current is Im = 2 A. Assuming the exponent of Bm to be 1.5, estimate Ph for Im = 0.5A and 8A.

Show that the force exerted on each charge, Q. Consider two 1-C charges sep...

Q. Consider two 1-C charges separated by 1 min free space. Show that the force exerted on each is about one million tons.

Determine the regulation of three-phase, A three-phase, six-pole, wye-conne...

A three-phase, six-pole, wye-connected synchronous generator is rated at 550 V and has a synchronous reactance Xs = 2 . When the generator supplies 50 kVA at rated voltage and a p

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd