Starting methods for polyphase induction motors, Electrical Engineering

Assignment Help:

Starting Methods for Polyphase Induction Motors

When high starting torques are required, a wound-rotor induction motor, with external resistances inserted in its rotor circuits, can be used. The starting current can be reduced and high values of starting torque per ampere of starting current can be obtained with rotor-resistance starting. The external resistances are generally cut out in steps as the machine runs up to speed.

For squirrel-cage-rotor machines, the problem is to keep down the starting current while maintaining adequate starting torque. The input current, for example, can be no more than 6 times the full-load current,while the starting torquemay be about 1.5 times the full-load torque.Depending on the capacity of the available supply system, direct-on-line starting may be suitable only for relatively small machines, up to 10-hp rating. Other starting methods include reduced-voltage starting by means of wye-delta starting, autotransformer starting, or stator-impedance starting.

883_Starting Methods for Polyphase Induction Motors.png

For employing the wye-delta starting method, a machine designed for delta operation is connected in wye during the starting period. Because the impedance between line terminals for wye connection is three times that for delta connection for the same line voltage, the line current at standstill for wye connection is reduced to one-third of the value for delta connection. Since the phase voltage is reduced by a factor of √3 during starting, it follows that the starting torque will be one-third of normal. For autotransformer starting, the setting of the autotransformer can be predetermined to limit the starting current to any desired value.An autotransformer,which reduces the voltage applied to the motor to x times the normal voltage, will reduce the starting current in the supply system as well as the starting torque of the motor to x2 times the normal values.

Stator-impedance starting may be employed if the starting-torque requirement is not severe. Series resistances (or impedances) are inserted in the lines to limit the starting current. These resistances are short-circuited out when the motor gains speed. This method has the obvious disadvantage of inefficiency caused by the extra losses in the external resistances.


Related Discussions:- Starting methods for polyphase induction motors

Find the total core loss, Q. Ac measurements with constant voltage amplitud...

Q. Ac measurements with constant voltage amplitude reveal that the total core loss of a certain magnetic circuit is 10 W at f = 50 Hz, and 13 Wat f = 60 Hz. Find the total core los

Find largest of n numbers stored in t memory, To determine the largest of n...

To determine the largest of n numbers stored into t memory, write a program in assembly language. A program of the largest of n numbers stored into t memory in assembly languag

Explain multimedia extensions technology, Explain MMX Technology. Mult...

Explain MMX Technology. Multimedia extensions technology adds 57 newly instructions to the instruction set of the Pentium - 4 microprocessors. The Multimedia extensions techno

Compute the efficiency of the motor, Q. A 10-hp, 230-V dc shunt motor takes...

Q. A 10-hp, 230-V dc shunt motor takes a full- load line current of 40 A. The armature and field resistances are 0.25 and 230 , respectively. The total brush-contact drop is 2 V,

Determine the percent voltage regulation of the transformer, The transforme...

The transformer of Example is supplying full load (i.e., rated load of 50 kVA) at a rated secondary voltage of 240 V and 0.8 power factor lagging. Neglecting the exciting current o

Find the initial and final values of the armature current, Q. A 7.5-hp, 250...

Q. A 7.5-hp, 250-V, 1800-r/min shuntmotor, having a full-load line current of 26 A, is started with a four-point starter. The resistance of the armature circuit, including the inte

3-phase 4 wire meters with ct and md, 3-Phase 4 Wire Meters with CT and MD ...

3-Phase 4 Wire Meters with CT and MD If load is commonly more than 50 A, CT operated meters should be used. It is to be remembered that CTs should be properly selected for acc

Realization of digital filter design, why we are going to realization of di...

why we are going to realization of digital filter after finding the H(z).

Interrupt signals - pins and signals , Interrupt Signals There are five...

Interrupt Signals There are five  interrupt  signals in 8085 microprocessor.  These  signals  are used to inter rut the  current  program  under  execution and  transfer the ex

Resistors, what are the classifications of fixed resistor?explain

what are the classifications of fixed resistor?explain

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd