Starting methods for polyphase induction motors, Electrical Engineering

Assignment Help:

Starting Methods for Polyphase Induction Motors

When high starting torques are required, a wound-rotor induction motor, with external resistances inserted in its rotor circuits, can be used. The starting current can be reduced and high values of starting torque per ampere of starting current can be obtained with rotor-resistance starting. The external resistances are generally cut out in steps as the machine runs up to speed.

For squirrel-cage-rotor machines, the problem is to keep down the starting current while maintaining adequate starting torque. The input current, for example, can be no more than 6 times the full-load current,while the starting torquemay be about 1.5 times the full-load torque.Depending on the capacity of the available supply system, direct-on-line starting may be suitable only for relatively small machines, up to 10-hp rating. Other starting methods include reduced-voltage starting by means of wye-delta starting, autotransformer starting, or stator-impedance starting.

883_Starting Methods for Polyphase Induction Motors.png

For employing the wye-delta starting method, a machine designed for delta operation is connected in wye during the starting period. Because the impedance between line terminals for wye connection is three times that for delta connection for the same line voltage, the line current at standstill for wye connection is reduced to one-third of the value for delta connection. Since the phase voltage is reduced by a factor of √3 during starting, it follows that the starting torque will be one-third of normal. For autotransformer starting, the setting of the autotransformer can be predetermined to limit the starting current to any desired value.An autotransformer,which reduces the voltage applied to the motor to x times the normal voltage, will reduce the starting current in the supply system as well as the starting torque of the motor to x2 times the normal values.

Stator-impedance starting may be employed if the starting-torque requirement is not severe. Series resistances (or impedances) are inserted in the lines to limit the starting current. These resistances are short-circuited out when the motor gains speed. This method has the obvious disadvantage of inefficiency caused by the extra losses in the external resistances.


Related Discussions:- Starting methods for polyphase induction motors

Static characteristics of the npn silicon bjt, Consider the common-emitter ...

Consider the common-emitter BJT circuit shown in Figure (a). The static characteristics of the npn silicon BJT are given in Figure (b) along with the load line. Calculate iB for v

Measure and set frequency by using an oscilloscope, 1. Introduction : ...

1. Introduction : Theory: Frequency is the number of occurrences of a repeating event per unit time. It can also be defined as the number of repetitions (cycles) of a w

Pins and signals , Pins  and Signals As  discussed  earlier that  808...

Pins  and Signals As  discussed  earlier that  8085  microprocessor  chip has 40 pins shown  various  pins  and signals of 8085  microprocessor. All  these  signals can be   c

DLD, draw alogic diagramto implement F=ABCDE using only 3 inputAND gates

draw alogic diagramto implement F=ABCDE using only 3 inputAND gates

Common emitter configuration, Common emitter configuration: even in co...

Common emitter configuration: even in common emitter configuration current relation is like is same like common bias configuration. For common emitter configuration output cha

Audio Amplifier, Hi, i''ve been given this task: You are required to desig...

Hi, i''ve been given this task: You are required to design a multi-stage audio amplifier with the following specification: Voltage gain 250 Input resistance 200 kOhm Output resi

Obtain the current by means of mesh-current analysis, By means of mesh-curr...

By means of mesh-current analysis, obtain the current in the 10-V source and the voltage across the 10- resistor in the circuit of Example.

Actual loading method, Actual Loading Method This method is employed c...

Actual Loading Method This method is employed commonly for testing of single phase meters within laboratory. On a meter testing bench that is equipped along with several taps

Edc, transistor biasing stabilization problems

transistor biasing stabilization problems

Saturation or active mode, Saturation or active mode While V GS  ...

Saturation or active mode While V GS   > V th  and  V DS   > (V GS   - V th ) The switch is turned on, and a channel has been made that allows current to flow

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd