What is the smallest size of A325 bolts required for the two plates in tension noted below, assuming the thickness of each plate is 1.0-in. and the applied force at each end is P=230 kips?

1812_Smallest Size of A325 bolts needed for two Plates in Tension.png

A) 5/8-in. Bolt

B) 3/4-in. Bolt

C) 0.875-in. Bolt

D) 1.0-in.Bolt

 


Related Discussions:- Smallest size of a325 bolts needed for two plates in tension

Raport, CASTE DISCRIMANIMATION

CASTE DISCRIMANIMATION

Basic considerations governing selection of road alignment, Basic Considera...

Basic Considerations Governing Selection of Road Alignment: The following considerations shall be kept in view in selecting the road alignment: Roads in Plain Areas (a)

Stress corrosion of pre-stressing steel, Stress corrosion of pre-stressing ...

Stress corrosion of pre-stressing steel Stress corrosion is crystalline cracking of metals under tensile stresses in the presence of corrosive agents. Conditions for stress cor

Define the meaning of circular prestressing, Define the meaning of circular...

Define the meaning of circular prestressing In circular prestressing, tendon wires are wrapped under tension over the concrete pipes which are pre-cast. The tension in the ten

Influence line, determine the maximum positive and negative shear shear

determine the maximum positive and negative shear shear

Is kerb necessary in road pavements, Question Is kerb necessary in road...

Question Is kerb necessary in road pavements? Answer In universal, kerbs are crucial in road pavements due to next cause- (i) They supply strength to sides of road

Bedding of precast concrete paving units, Q. Sand layer vs. cement sand use...

Q. Sand layer vs. cement sand used as bedding of precast concrete paving units Cement sand is a mixture of sand and cement and it behaves as a cohesive mass once mixed. Usuall

Water absorption test for precast concrete pipes, Purpose of carrying out w...

Purpose of carrying out water absorption test for precast concrete pipes Cement will mix with more water than is essential to ultimately combine during hydration of cement pas

Aana

6/1/2013 2:20:05 AM

Answer: Since there are only two plates shown, the bolts are in single shear. The available bolt strength for A325 bolts at the strength limit state is dependent on if the threads are in the shear plane or not. It is conservative to assume that they are if it is not explicitly stated in the problem. Thus, assume the threads are in the shear plane. The shear force per bolt is then:

Vbolt = 230 kip / 11 bolts = 20.9 kips. The required bolt size for this shear strength is 21.6 kips per bolt for a 7/8" section. Note-the problem did not use the 1" thickness.

The answer is C) 7/8-in. bolt 