Process control, Chemical Engineering

Assignment Help:

1.      In the system shown schematically below, water is supplied to a spray nozzle by a gear pump with a constant output of 20 US gpm. The flow rate of water discharged through the nozzle is controlled by manipulating the flow of water re-circulated around the pump using a proportional-plus-integral controller. The set point of the controller is normally 14 US gpm but can vary between 9 and 18 US gpm. The flow sensor has a range of 0-20 US gpm and responds instantaneously to flow variations. The control valve has a CV of 3 US gpm/psi1/2, a time constant of 2 seconds, a linear installed characteristic and is current-to-close.

(a) What should be the action of She controller (reverse or direct)? Why?

(b) Would it be better to eliminate the recirculation loop and install the control valve immediately downstream of the pump? Why?

(c) If the pump discharge pressure is 100 psig when the control valve is closed, show that the flow rate across the nozzle is 8 US gpm when the control valve is wide open,

Notes: The valve and nozzle are the only significant flow resistances in this system. You may also assume that the pump suction port and the spray leaving the nozzle are at atmospheric pressure. The nozzle behaves as an orifice.

(d) What are the outputs of the controller and flow transmitter (in %) when the set point is 12 US gpm and steady-state has been achieved?

148_Process Control.png


Related Discussions:- Process control

Explain brazing and soldering, Brazing and Soldering - Both soldering and ...

Brazing and Soldering - Both soldering and brazing processes are useful for combination two dissimilar metals. Both brazing alloy and solder have lower melting points than the met

Chemistry separate the mixture of sand and naphthale, chemistry separate th...

chemistry separate the mixture of sand and naphthalene by sublimation

Solvent extraction system, how to design Extractive or Extraction colum and...

how to design Extractive or Extraction colum and solvent dehydrating columns

Water Treatment, Among phosphate and calgon methods, which one would be the...

Among phosphate and calgon methods, which one would be the best option for internal conditioning

Effluent treatment, how to reduce COD in primary process effluent treatment...

how to reduce COD in primary process effluent treatment system

Corrosion ., the pilling bedworth ratio of iron is 1.77 why it not stable a...

the pilling bedworth ratio of iron is 1.77 why it not stable as per rulr

THIN LAYER CHROMATOGRAPHY, how do you prepare and use preparatory thin lay...

how do you prepare and use preparatory thin layer chromatography plates

A commercial aircraft skin material, Normal 0 false false ...

Normal 0 false false false EN-IN X-NONE X-NONE

Heat transfer coefficient for the forced convection , A) A horizontal tube ...

A) A horizontal tube having a 1.25 cm outside diameter is submerged in a water 1 atm and 100 oC. Determine the heat flux for the surface temperature of (a) 540 o C, (b) 650 o C,

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd