New Assembly Buildings:

12.1.1.1 The requirements of this chapter shall apply to new buildings or portions thereof used as an assembly occupancy.

12.1.3.2 Simultaneous Occupancy. Exits shall be sufficient for simultaneous occupancy of both the assembly occupancy and other parts of the building, except where the

authority having jurisdiction determines that the conditions are such that simultaneous occupancy will not occur.

12.1.6 Minimum Construction Requirements. Assembly occupancies shall be limited to

the building construction types specified in Table 12.1.6, based on the number of stories in height as defined in 4.6.3, unless otherwise permitted by the following: (1) This requirement shall not apply to outdoor grandstands of Type I or Type II construction.

(2) This requirement shall not apply to outdoor grandstands of Type III, Type IV, or

Type V construction that meet the requirements of 12.4.8.

(3) This requirement shall not apply to grandstands of non-combustible construction supported by the floor in a building meeting the construction requirements of Table

12.1.6.

(4) This requirement shall not apply to assembly occupancies within mall buildings in accordance with 36.4.4.

12.1.7.1 General. The occupant load, in number of persons for whom means of egress

and other provisions are required, shall be determined on the basis of the occupant load factors of Table 7.3.1.2 that are characteristic of the use of the space or shall be determined as the maximum probable population of the space under consideration, whichever is greater.

12.1.7.1.1 In areas not in excess of 930 m2, the occupant load shall not exceed one person in 0.46 m2.

12.1.7.1.2 In areas in excess of 930 m2, the occupant load shall not exceed one person in 0.65 m2.

12.1.7.2 Waiting Spaces. In theaters and other assembly occupancies where persons are admitted to the building at times when seats are not available, or when the

permitted occupant load has been reached based on 12.1.7.1 and persons are allowed to wait in a lobby or similar space until seats or space is available, all of the following

requirements shall apply:

(1) Such use of a lobby or similar space shall not encroach upon the required clear width of exits.

(2) The waiting spaces shall be restricted to areas other than the required means of egress.

(3) Exits shall be provided for the waiting spaces on the basis of one person for each 0.28 m2 of waiting space area.

 


Related Discussions:- New assembly buildings - fire protection engineering

Material science, Ask question #Minimum lkjhbi mbj jhb uy 100 words accept...

Ask question #Minimum lkjhbi mbj jhb uy 100 words accepted#

Keplers’s three laws of planetary motion, Expertsmind.com brings you uniqu...

Expertsmind.com brings you unique solution in electrical engineering -          Ancient people kept track of time and seasons as it affected agriculture. -          Some

Robotics, how to become robotics engneer

how to become robotics engneer

MICRO PROCESSOR, Describe the operation an 8086 will perform when it excute...

Describe the operation an 8086 will perform when it excutes ADD AX,BX

Business Management Techniques -Company organisation, Business functions of...

Business functions of engineering firm 2.1-Engineering business: 2.2- Functions of engineering business

Thermo electric thermometer, how thermoelecteric thermometer is contructed ...

how thermoelecteric thermometer is contructed and how it working

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd