The devices in power system shown in Figure 2 have the following ratings:

G1 : 100 MVA, 13.8 kV grounded Y, X” = 0.15 pu, X2 = 0.015 pu Xo = 0.05 pu
G2 : 50 MVA, 20.0 kV grounded Y, X” = 0.15 pu, X2 = 0.015 pu Xo = 0.05 pu
T1 : 100 MVA, 13.8/138 kV (both grounded), X1 = 0.08 pu, X2 = 0.08 pu Xo = 0.08 pu
T2 : 50 MVA, 20.0/138 kV, ?-Y grounded Y, X1 = 0.08 pu, X2 = 0.08 pu Xo = 0.08 pu
L1 : 100 MVA, 138 kV grounded X1 = 19 ?, X2 = 19 ?, Xo = 50 ?,


Figure 2

Assume that all resistances in the power system can be neglected. The system base apparent power is ____ (to be specified by your lecturer)MVA, and the base line voltage is 13.8 kV at bus 1. Assume that the voltage at bus 1 is 13.8 kV and that the power system is initially unloaded.

2. Use Matlab to:

a. Find the sub transient per-phase equivalent circuits of this power system for positive-, negative- and zero-sequence component.

b. Find the subtransient fault current at the fault found at the location indicated by X for:



i) A symmetrical three-phase fault
ii) A single line-to-ground fault
iii) A line-to-line fault
iv) A double line-to-ground fault

(A student will solving for the transient fault line current for two (2) types of fault to be specified by the lecturer).

Related Discussions:- MATLAB support for fault analysis in transmission lines

Digital system, 1- Use 4-to-16 decoder and some residue gates to recognize ...

1- Use 4-to-16 decoder and some residue gates to recognize the following functions F1(A,B,C)= S(1,2,4,5,7) F2(A,B,C,D)= S(1,2,4,5,7,10,12,14,15) F3(A,B,C,D,E)= S(1,2,4,5,7,10,12,1

Forces and torques in magnetic-field systems, Q. Forces and torques in magn...

Q. Forces and torques in magnetic-field systems? We mentioned earlier that the greater ease of storing energy in magnetic fields largely accounts for the common use of electrom

Solution manual, Ask question #Minimum 100 words accespted#i want solution ...

Ask question #Minimum 100 words accespted#i want solution manual of electronic instrumentation and measurements

Amperes circuital law, Amperes Circuital Law The    observation    tha...

Amperes Circuital Law The    observation    that    magnetic    field strength varied with distance from the wire led to the following statement: 'If  the  magnetic  field

Motor, What is the main function of the slip ring

What is the main function of the slip ring

Power system engineering, A three-phase transposed line is composed of one ...

A three-phase transposed line is composed of one ACSR conductor per phase with flat horizontal spacing of 11 meters as shown in Figure (a). The conductors have a diameter of 3.625

Power engineering, is electrical power more important in the world than oth...

is electrical power more important in the world than other streams?

Parallel - flash converter, Q. Parallel - flash converter? Parallel / ...

Q. Parallel - flash converter? Parallel / flash converter. Also known as parallel A/D converter, this circuit is the simplest to understand. It's formed of a series of co

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd