In construction of a two-span bridge (span length = L) by using span-by-span construction, why is the length of about 1.25L bridge segment is constructed in first phase of construction?


Related Discussions:- Length is constructed in first phase of construction

Define the both inside clearance and outside clearance, The inner diameters...

The inner diameters of a sampling tube and that of a cutting edge are 70 mm and 68 mm correspondingly, their outer diameters are 72 and 74 mm respectively. Verify the inside cle

Doors, types of doors with there prices

types of doors with there prices

Premix carpet - road pavements, Premix Carpet: An open graded premix ...

Premix Carpet: An open graded premix carpet, commonly called premix carpet (PC), is an open graded premixed material laid to a thickness of 20 mm and rolled, followed by a se

Raport, CASTE DISCRIMANIMATION

CASTE DISCRIMANIMATION

Can u give me a sample assignment, im newer to the courses so i would like ...

im newer to the courses so i would like to know about the assignment types. in this case can u please show me a sample assignment?

Explain energy grade line (egl), Explain Energy Grade Line (EGL) Graph ...

Explain Energy Grade Line (EGL) Graph of the sum of the potential, pressure and kinetic energies along a pipe or open channel. Energies are plotted along the y-axis above a dat

How to determine the water content and bulk density, The wet weight of a sa...

The wet weight of a sample is missing in a Proctor test. The oven-dry weight of this sample is 189 N. The volume of the mould used is 1000 cm 3 . If the degree of saturation of

Dimples in polytetrafluoroethylene, Dimples in Polytetrafluoroethylene (PTF...

Dimples in Polytetrafluoroethylene (PTFE) PTFE is a fluorocarbon polymer that possesses good chemical resistance and can function in a wide range of temperature. The most signi

Hydraulics, In this question we consider a bended outlet of pipe flow AB. E...

In this question we consider a bended outlet of pipe flow AB. End A is attached to an incoming pipe by a flange connection. The pipe diameter at A is the same as the incoming pipe,

12/5/2013 6:44:00 AM

Mostly, there are primarily three reasons for this arrangement-
(i) Permanent structure is statically indeterminate structure. all through construction by using span-by-span construction, if first stage of construction contains of first span length L only, then a sagging moment in mid span of partially completed bridge is big than that of completed two-span permanent structure.
To pass up such occurrence, 0.25L of bridge segment is extended further from second pier which offers a counteracting moment, thereby reducing mid-span moment of partially completed bridge.
(ii) The place of 1.25 L countering from first pier is approximate location of point of contra flexure, imagine that two-span Bridge is uniformly loaded in which bridge moment about zero in an event of future is loaded bridge.
Therefore, designing of construction joint in this particular location has least adverse effect on structural performance of a bridge.
(iii) In case of a pre stressed bridge, pre stressing work has to be carried out after construction of first segment of bridge. If pre stressing work is performed at first pier which is heavily reinforced with reinforcement, it is adverse when compared with pre stressing location at 1.25L from first pier everywhere there is relatively new space to accommodate pre stressing works.

12/5/2013 6:45:29 AM

Mostly, there are primarily three reasons for this arrangement-
(i) Permanent structure is statically indeterminate structure. all through construction by using span-by-span construction, if first stage of construction contains of first span length L only, then a sagging moment in mid span of partially completed bridge is big than that of completed two-span permanent structure.
To pass up such occurrence, 0.25L of bridge segment is extended further from second pier which offers a counteracting moment, thereby reducing mid-span moment of partially completed bridge.
(ii) The place of 1.25 L countering from first pier is approximate location of point of contra flexure, imagine that two-span Bridge is uniformly loaded in which bridge moment about zero in an event of future is loaded bridge.
Therefore, designing of construction joint in this particular location has least adverse effect on structural performance of a bridge.
(iii) In case of a pre stressed bridge, pre stressing work has to be carried out after construction of first segment of bridge. If pre stressing work is performed at first pier which is heavily reinforced with reinforcement, it is adverse when compared with pre stressing location at 1.25L from first pier everywhere there is relatively new space to accommodate pre stressing works.