Find the real and reactive powers per phase, Electrical Engineering

Assignment Help:

Q. A 345-kV, 60-Hz, three-phase transmission line delivers 600 MVA at 0.866 power factor lagging to a three-phase load connected to its receiving- end terminals. Assuming that the voltage at the receiving end is 345 kV and the load is wye- connected, find the following:

(a) Complex load impedance per phase ¯ ZL/ph.

(b) Line and phase currents.

(c) Real and reactive powers per phase.

(d) Total three-phase real and reactive powers.


Related Discussions:- Find the real and reactive powers per phase

Determine which is the sinusoidal expression for the current, 1. The voltag...

1. The voltage across a 1 - μF capacitor is given. Which is the sinusoidal expression for the current? a) 30 sin200t b) 70cos (800t - 20°) 2. At what frequency will the re

Electromechanical and electronic switching system, Q. Compare electromechan...

Q. Compare electromechanical switching system with electronic switching system. Sr. No Electromechanical switching System Electroni

Signal., explain about signal

explain about signal

Explain fourier series, Q. Explain Fourier Series? The phasor method of...

Q. Explain Fourier Series? The phasor method of circuit analysis can be extended (by using the principle of superposition) to find the response in linear systems due to nonsinu

Load balancing and load management, Load Balancing and Load Management ...

Load Balancing and Load Management It has been observed in which the load on all three phases of a distribution line and between the feeders is not balanced. This output in in

Single direction pump, Modify the design of the circuit shown in FIGURE and...

Modify the design of the circuit shown in FIGURE and draw a circuit diagram to provide rotary actuation in both directions using a single direction pump (to replace the bi-directio

Output characteristics , Output Characteristics The output  or drain  ...

Output Characteristics The output  or drain  characteristic of N - Channel  power MOSFET. When gate  is made positive with respect to the source an N type  channel  is formed

Explain load flow analysis, Explain Load Flow Analysis The method commo...

Explain Load Flow Analysis The method commonly used for load flow analysis is the nodal analysis. The nodal analysis method is given in many books on circuit theory and is base

Uninterruptable power supply , Uninterruptable power  Supply An unint...

Uninterruptable power  Supply An uninterruptible  power supply  provides emergency power when  utility power  is not  available. It  maintains the supply  under  all condition

Explain indirect data addressing mode, Explain indirect data addressing mod...

Explain indirect data addressing mode (with examples) available in microprocessors. Indirect Mode: Address given in instruction includes address where the operand resi