Explain synchronisation and parallel operation, Electrical Engineering

Assignment Help:

Explain Synchronisation and Parallel Operation

Generation, transmission and distribution of electric power have to be conducted in an efficient and reliable way at a reasonable cost with the least amount of interruptions. Consequently, in a large power system many synchronous generators are connected in parallel to a common line known as an infinite bus of fixed voltage and frequency, and pre-determined phase sequence. A number of safety requirements need to be satisfied prior to connecting a generator to the infinite bus (this is called a synchronising procedure):

2448_Explain Synchronisation and Parallel Operation.png

(1) The operating frequency,

(2) The line voltage and

(3) The phase sequence must all be the same as those for an infinite bus.

To meet an increased load demand, let us, for instance, bring a second generator into service as shown in Figure. The necessary synchronisation procedure consists of the following major steps. The speed of the incoming generator is adjusted to obtain the frequency of the induced voltage equal to that of the infinite bus. Now that the frequency match is achieved the field current can be raised to a level at which the induced voltage of the second generator is identical to the bus voltage. In order to verify the phase sequence, three lamps are connected asymmetrically as illustrated in the figure. When the phase sequence is correct, the lamp LI will be dark, while the other two lamps will glow brightly. If the phase sequence is not proper, all the lamps will glow or become dark simultaneously. When all the above conditions are met, the second generator can be safely connected to the infinite bus by closing the appropriate circuit breaker.

In addition to the lamps to check the conditions for synchronism, an electronic device (often computer controlled) called a synchroscope is also used to perform a precise switching when the above criteria are fulfilled. It provides the information on the incoming generator as to whether it is running at a lower or higher speed. At a proper speed and a correct phase sequence, the synchroscope indicates zero when the synchronising switch must be closed to connect the second generator on line. At this moment, it is neither receiving nor delivering any power. This is referred to as the floating stage of the generator. If we now increase the field current, the second generator will produce reactive power and help improve voltage regulation. Else, if an attempt is made to increase the rotor speed, the torque developed will increase and the second generator will begin to supply active power to the load.


Related Discussions:- Explain synchronisation and parallel operation

Factors of contributing to losses in service cables, Factors of Contributin...

Factors of Contributing to Losses in Service Cables 1. Tapping of underground service cables: The service cables must be visible so that tapping of cables can be detected. U

The resistance of an 8 m length of the same wire, The resistance of a 5 m l...

The resistance of a 5 m length of wire is 600Ω.Determine: a)  the resistance of an 8 m length of the same wire, b)  the length of the same wire when the resistance is 420Ω

Compute the motor speed, Consider the 220-V, 1800-r/min dc motor, controlle...

Consider the 220-V, 1800-r/min dc motor, controlled by a three-phase fully controlled rectifier from a 60-Hz ac source. The armature-circuit resistance and inductance are 1.5  and

Show common signal-processing operations, Q. Show Common signal-processing ...

Q. Show Common signal-processing operations? Common signal-processing operations include the following: • Amplification to compensate for attenuation • Filtering to reduc

Increase in ht and lt ratio, Increase in HT and LT Ratio It is well kn...

Increase in HT and LT Ratio It is well known that for high HT/LT ratio, the losses will be low. The losses for a given quantum of power supplied through a line are inversely p

Hold input - externally initiated signals , HOLD Input This  signal (W...

HOLD Input This  signal (When  goes high ) indicates that  other device ( such as DMA Controller) is requesting the  use of  address and data buses. DMA controller is  explaine

ECE, a problem solving problem

a problem solving problem

Determine excitation voltage and power angle, A 500KVA, 6 pole, 500v, 3 pha...

A 500KVA, 6 pole, 500v, 3 phase, wye-connected synchronous generator has a synchronous impedance of 0.1 + j1.5 ohms per phase. If the generator is driven at 1000 r.p.m., what is th

Explain about transistor amplifiers, Q. Explain about Transistor Amplifiers...

Q. Explain about Transistor Amplifiers? Amplifiers are circuits that produce an output signal which is larger than, but proportional to, an input signal. The input and output s

Inverting comparator, what is the graph of inverting comparator,if input vo...

what is the graph of inverting comparator,if input voltage less than reference voltage

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd