Explain Synchronisation and Parallel Operation

Generation, transmission and distribution of electric power have to be conducted in an efficient and reliable way at a reasonable cost with the least amount of interruptions. Consequently, in a large power system many synchronous generators are connected in parallel to a common line known as an infinite bus of fixed voltage and frequency, and pre-determined phase sequence. A number of safety requirements need to be satisfied prior to connecting a generator to the infinite bus (this is called a synchronising procedure):

2448_Explain Synchronisation and Parallel Operation.png

(1) The operating frequency,

(2) The line voltage and

(3) The phase sequence must all be the same as those for an infinite bus.

To meet an increased load demand, let us, for instance, bring a second generator into service as shown in Figure. The necessary synchronisation procedure consists of the following major steps. The speed of the incoming generator is adjusted to obtain the frequency of the induced voltage equal to that of the infinite bus. Now that the frequency match is achieved the field current can be raised to a level at which the induced voltage of the second generator is identical to the bus voltage. In order to verify the phase sequence, three lamps are connected asymmetrically as illustrated in the figure. When the phase sequence is correct, the lamp LI will be dark, while the other two lamps will glow brightly. If the phase sequence is not proper, all the lamps will glow or become dark simultaneously. When all the above conditions are met, the second generator can be safely connected to the infinite bus by closing the appropriate circuit breaker.

In addition to the lamps to check the conditions for synchronism, an electronic device (often computer controlled) called a synchroscope is also used to perform a precise switching when the above criteria are fulfilled. It provides the information on the incoming generator as to whether it is running at a lower or higher speed. At a proper speed and a correct phase sequence, the synchroscope indicates zero when the synchronising switch must be closed to connect the second generator on line. At this moment, it is neither receiving nor delivering any power. This is referred to as the floating stage of the generator. If we now increase the field current, the second generator will produce reactive power and help improve voltage regulation. Else, if an attempt is made to increase the rotor speed, the torque developed will increase and the second generator will begin to supply active power to the load.


Related Discussions:- Explain synchronisation and parallel operation

Calculate the induced voltage, Q. A four-pole, lap-wound armature has 144 s...

Q. A four-pole, lap-wound armature has 144 slots with two coil sides per slot, each coil having two turns. If the flux per pole is 20 mWb and the armature rotates at 720 r/min, cal

Write discussion on Construction and working of analog type, Write discussi...

Write discussion on Construction and working of analog type storage oscilloscope

Features of modern ic engines, The IC engine based automobiles have been bu...

The IC engine based automobiles have been built and sold for more than 100 years. Predominantly the fuels used for running these IC engines have been petrol and diesel. In recent t

Application platform requirement - gis technology, Software/Application Pla...

Software/Application Platform Requirement: GIS solutions would primarily consist of Database and Applications software. The application package should work in LAN/WAN/Interne

RLC series, What is Average value in AC circuit?

What is Average value in AC circuit?

Differential amplifier, Ask question #Minimum 100 words What is neeed of d...

Ask question #Minimum 100 words What is neeed of differential amplifier

Explain interrupts of 8085, Explain Interrupts of 8085. a) Maskable  in...

Explain Interrupts of 8085. a) Maskable  interrupt b)  Vectored interrupt c)  Non maskable interrupt d) Hardware interrupt e)  Software interrupt

Calculate minimum number of poles for the induction machine, A wound-rotor ...

A wound-rotor induction machine, driven by a dc motor whose speed can be controlled, is operated as a frequency changer. The three-phase stator winding of the induction machine is

Classify the materials based on the energy bands, Classify the materials ba...

Classify the materials based on the energy bands and explain them. Classification of materials based on energy bands: With reference to various band structures demonstrate

Find the current and voltage drop at resistor, For the circuit in figure, f...

For the circuit in figure, find the current and voltage drop at every resistor

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd