Explain synchronisation and parallel operation, Electrical Engineering

Assignment Help:

Explain Synchronisation and Parallel Operation

Generation, transmission and distribution of electric power have to be conducted in an efficient and reliable way at a reasonable cost with the least amount of interruptions. Consequently, in a large power system many synchronous generators are connected in parallel to a common line known as an infinite bus of fixed voltage and frequency, and pre-determined phase sequence. A number of safety requirements need to be satisfied prior to connecting a generator to the infinite bus (this is called a synchronising procedure):

2448_Explain Synchronisation and Parallel Operation.png

(1) The operating frequency,

(2) The line voltage and

(3) The phase sequence must all be the same as those for an infinite bus.

To meet an increased load demand, let us, for instance, bring a second generator into service as shown in Figure. The necessary synchronisation procedure consists of the following major steps. The speed of the incoming generator is adjusted to obtain the frequency of the induced voltage equal to that of the infinite bus. Now that the frequency match is achieved the field current can be raised to a level at which the induced voltage of the second generator is identical to the bus voltage. In order to verify the phase sequence, three lamps are connected asymmetrically as illustrated in the figure. When the phase sequence is correct, the lamp LI will be dark, while the other two lamps will glow brightly. If the phase sequence is not proper, all the lamps will glow or become dark simultaneously. When all the above conditions are met, the second generator can be safely connected to the infinite bus by closing the appropriate circuit breaker.

In addition to the lamps to check the conditions for synchronism, an electronic device (often computer controlled) called a synchroscope is also used to perform a precise switching when the above criteria are fulfilled. It provides the information on the incoming generator as to whether it is running at a lower or higher speed. At a proper speed and a correct phase sequence, the synchroscope indicates zero when the synchronising switch must be closed to connect the second generator on line. At this moment, it is neither receiving nor delivering any power. This is referred to as the floating stage of the generator. If we now increase the field current, the second generator will produce reactive power and help improve voltage regulation. Else, if an attempt is made to increase the rotor speed, the torque developed will increase and the second generator will begin to supply active power to the load.


Related Discussions:- Explain synchronisation and parallel operation

Determine gold and silver are which type of materials, Gold and silver are ...

Gold and silver are (A) Dielectric materials (B) Low resistivity conducting materials. (C) Magnetic materials. (D) Insulating materials. Ans: Gold and si

Compute the transfer function from the input, In this project we will consi...

In this project we will consider the control of a synchronous generator supplying electricity to the grid. We will focus on the problem of frequency stability. The frequency at whi

Condition return, Condition Return Similar to conditional jump and cal...

Condition Return Similar to conditional jump and call  instructions there are conditional return  instructions  also  based on various  flags.

Defective metering and meter reading errors, Defective Metering and Meter R...

Defective Metering and Meter Reading Errors Defective Metering Tampered, slow running, stalled, damaged meters are a cause of huge losses to the utility. The electromecha

Name the modes used by the dma processor to transfer data, Name the three m...

Name the three modes used by the DMA processor to transfer data? The three modes are:- a) Signal transfer mode (cycling stealing mode) b) Block transfer mode c) Demand

Explain 8259 pin diagram, Explain 8259 Pin Diagram. The 8259A adds 8 ve...

Explain 8259 Pin Diagram. The 8259A adds 8 vectored priority encoded interrupts to the microprocessor. It can be expanded to 64 interrupt requests by using one master 8259A and

Show effects of saliency and saturation, Q. Show Effects of Saliency and Sa...

Q. Show Effects of Saliency and Saturation? Because of saliency, the reactancemeasured at the terminals of a salient-pole synchronousmachine as opposed to a cylindrical-rotor m

Transformer, 1 diagram basic layout of a simple transformer

1 diagram basic layout of a simple transformer

Determine current for a bjt, Q. For a BJT with vBE = 0.7V, I CBO = 4 nA, ...

Q. For a BJT with vBE = 0.7V, I CBO = 4 nA, i E = 1 mA, and i C = 0.9 mA, evaluate α, iB,iSE, and β.

Derive the transfer function, A data hold is to be constructed that reconst...

A data hold is to be constructed that reconstructs the sampled signal by the straight-line approximation shown in Figure. Note that this device is a polygonal data hold with a dela

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd