Explain balanced wye-connected load, Electrical Engineering

Assignment Help:

Balanced Wye-Connected Load

Let us consider a three-phase, four-wire 208-V supply system connected to a balanced wye connected load with an impedance of 10 20° , as shown in Figure (a). We shall solve for the line currents and draw the corresponding phasor diagram.

Conventionally it is assumed that 208 V is the rms value of the line-to-line voltage of the supply system, and the phase sequence is positive, or A-B-C, unless mentioned otherwise. The magnitude of the line-to-neutral (or phase) voltages is given by 208/√3, or 120 V. Selecting the line currents returning through the neutral conductor, as shown in Figure, we have

1407_Balanced Wye-Connected Load.png

Note that ¯VBC has been chosen arbitrarily as the reference phasor, as in Figure (b). Assuming the direction of the neutral current toward the load as positive, we obtain

1532_Balanced Wye-Connected Load1.png

That is to say that the system neutral and the star point of the wye-connected load are at the same potential, even if they are not connected together electrically. It makes no difference whether they are interconnected or not.

Thus, for a balanced wye-connected load, the neutral current is always zero. The line currents and phase currents are equal inmagnitude, and the line currents are in phasewith the corresponding phase currents. The line-to-line voltages, in magnitude, are √3 times the phase voltages, and the phase voltages lag the corresponding line voltages by 30°.

The phasor diagram is drawn in Figure(b), from which it can be observed that the balanced line (or phase) currents lag the corresponding line-to-neutral voltages by the impedance

55_Balanced Wye-Connected Load2.png

angle (20° in our example). The load power factor is given by cos 20° for our problem, and it is said to be lagging in this case, as the impedance angle is positive and the phase current lags the corresponding phase voltage by that angle.

The problem can also be solved in a simpler way by making use of a single-line equivalent circuit, as shown in Figure(c),

303_Balanced Wye-Connected Load3.png

in which ¯ VL-N is chosen as the reference for convenience. The magnitude of the line current and the power factor angle are known; the negative sign associated with the angle indicates that the power factor is lagging. By knowing that the line (or phase) currents ¯IA, ¯IB, ¯IC lag their respective voltages ¯VAN, ¯VBN, and ¯VCN by 20°, the phase angles of various voltages and currents, if desired, can be obtained with respect to any chosen reference, such as ¯VBC.


Related Discussions:- Explain balanced wye-connected load

Compute the mean torque, Q. A rotating electric machine with uniform air ga...

Q. A rotating electric machine with uniform air gap has a cylindrical rotor winding with inductance L 2 =1 H and a stator winding with inductance L 1 =3H. Themutual inductance va

Determine speed of the rotor field relative to rotor winding, Abalanced thr...

Abalanced three-phase, 60-Hz voltage is applied to a three-phase, two-pole induction motor. Corresponding to a per-unit slip of 0.05, determine the following: (a) The speed of t

8. A road 300 m long is required to be illuminated b, Ask questio8. A road ...

Ask questio8. A road 300 m long is required to be illuminated by providing 40W fluorescent lamps. The width of the road is 4m. Design a street lighting scheme for obtaining minimu

Explain the transfer characteristics, Q. Explain the transfer characteristi...

Q. Explain the transfer characteristics in a few words ? The transfer characteristics are a plot of an output (or a drain) current versus an input controlling quantity. There i

Calculate the iron loss, Q. The efficiency of a 400-kVA, single-phase, 60-H...

Q. The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8 power factor, and 99.13%with half rated current at unity power fa

Discrete time system transfer function, For a discrete time unit step input...

For a discrete time unit step input x(kT), the output  y(kT) of a system is shown below,   Part (a)  Obtain the Z-transform of the output signal y(kT).   Part (b)   F

Incorrect Solution, Hi there i just asked for question and answer for 5 cha...

Hi there i just asked for question and answer for 5 chapter and i just receive some of them in word the rest are in apiece of paper which is unprofessional could you please have l

Find the total current and total resistance, For the circuit in figure, fin...

For the circuit in figure, find: a)  Total resistance b)  Total current c)  Current flow through resistor 6Ω and 4Ω

Calculate the e.m.f. generated in armature of a d.c. machine, The armature ...

The armature of a d.c. machine has a resistance of 0.3 and is connected to a 200V supply. Calculate the e.m.f. generated when it is running (a) as a generator giving 80A (b) as a

Develop a block diagram of an asynchronous decade counter, Q. Counting to m...

Q. Counting to moduli other than 2 n is a frequent requirement, the most common being to count through the binary-coded decimal (BCD) 8421 sequence. All that is required is a four

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd