Explain balanced wye-connected load, Electrical Engineering

Assignment Help:

Balanced Wye-Connected Load

Let us consider a three-phase, four-wire 208-V supply system connected to a balanced wye connected load with an impedance of 10 20° , as shown in Figure (a). We shall solve for the line currents and draw the corresponding phasor diagram.

Conventionally it is assumed that 208 V is the rms value of the line-to-line voltage of the supply system, and the phase sequence is positive, or A-B-C, unless mentioned otherwise. The magnitude of the line-to-neutral (or phase) voltages is given by 208/√3, or 120 V. Selecting the line currents returning through the neutral conductor, as shown in Figure, we have

1407_Balanced Wye-Connected Load.png

Note that ¯VBC has been chosen arbitrarily as the reference phasor, as in Figure (b). Assuming the direction of the neutral current toward the load as positive, we obtain

1532_Balanced Wye-Connected Load1.png

That is to say that the system neutral and the star point of the wye-connected load are at the same potential, even if they are not connected together electrically. It makes no difference whether they are interconnected or not.

Thus, for a balanced wye-connected load, the neutral current is always zero. The line currents and phase currents are equal inmagnitude, and the line currents are in phasewith the corresponding phase currents. The line-to-line voltages, in magnitude, are √3 times the phase voltages, and the phase voltages lag the corresponding line voltages by 30°.

The phasor diagram is drawn in Figure(b), from which it can be observed that the balanced line (or phase) currents lag the corresponding line-to-neutral voltages by the impedance

55_Balanced Wye-Connected Load2.png

angle (20° in our example). The load power factor is given by cos 20° for our problem, and it is said to be lagging in this case, as the impedance angle is positive and the phase current lags the corresponding phase voltage by that angle.

The problem can also be solved in a simpler way by making use of a single-line equivalent circuit, as shown in Figure(c),

303_Balanced Wye-Connected Load3.png

in which ¯ VL-N is chosen as the reference for convenience. The magnitude of the line current and the power factor angle are known; the negative sign associated with the angle indicates that the power factor is lagging. By knowing that the line (or phase) currents ¯IA, ¯IB, ¯IC lag their respective voltages ¯VAN, ¯VBN, and ¯VCN by 20°, the phase angles of various voltages and currents, if desired, can be obtained with respect to any chosen reference, such as ¯VBC.


Related Discussions:- Explain balanced wye-connected load

Explain basic input output system function call, Discuss BIOS function call...

Discuss BIOS function call with one example. BIO stands for Basic Input Output System: This is a set of programs to give most basic low-level services as services keyboard, s

What are the different parameters of jfet, Q. What are the different parame...

Q. What are the different parameters of jfet ? A bipolar junction transistor (BJT) is a current controlled device that is output characteristics of the device are controlled by

About semi conductor, explain compensation and charge neutrality in GaAs

explain compensation and charge neutrality in GaAs

Three phase induction motors - motor control , Three Phase Induction Motors...

Three Phase Induction Motors A three  phase induction rotor  consists  a stators  and a motor stator has balanced three  phase  winding. These windings  are distributed in the

Relative and absolute motion measuring device, a) With the help of a neat a...

a) With the help of a neat and clean sketch illustrate the difference between relative and absolute motion measuring device. b) Discuss electromechanical methods for calculating

What is an usart, What is an USART? USART stands for universal synchron...

What is an USART? USART stands for universal synchronous/Asynchronous Receiver/ Transmitter. It is a programmable communication interface that can communicate by using either s

Grade of service in loss systems, Q. Grade of Service In loss systems? ...

Q. Grade of Service In loss systems? Grade of Service : In loss systems, traffic carried by the network is normally lower than actual traffic offered to the network by subscri

Compute the terminal voltage and current of each generator, Q. Three dc gen...

Q. Three dc generators are operating in parallel with excitations such that their external characteristics are almost straight lines over the working range with the following pairs

Determine the equivalent winding resistance, Determine the equivalent windi...

Determine the equivalent winding resistance: A 50 kVA, 2200/110 V, 50 HZ' transformer contain an HV winding resistance of 0.15 Ω and a leakage reactance of 0.45 Ω. The LV wind

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd