Explain balanced wye-connected load, Electrical Engineering

Assignment Help:

Balanced Wye-Connected Load

Let us consider a three-phase, four-wire 208-V supply system connected to a balanced wye connected load with an impedance of 10 20° , as shown in Figure (a). We shall solve for the line currents and draw the corresponding phasor diagram.

Conventionally it is assumed that 208 V is the rms value of the line-to-line voltage of the supply system, and the phase sequence is positive, or A-B-C, unless mentioned otherwise. The magnitude of the line-to-neutral (or phase) voltages is given by 208/√3, or 120 V. Selecting the line currents returning through the neutral conductor, as shown in Figure, we have

1407_Balanced Wye-Connected Load.png

Note that ¯VBC has been chosen arbitrarily as the reference phasor, as in Figure (b). Assuming the direction of the neutral current toward the load as positive, we obtain

1532_Balanced Wye-Connected Load1.png

That is to say that the system neutral and the star point of the wye-connected load are at the same potential, even if they are not connected together electrically. It makes no difference whether they are interconnected or not.

Thus, for a balanced wye-connected load, the neutral current is always zero. The line currents and phase currents are equal inmagnitude, and the line currents are in phasewith the corresponding phase currents. The line-to-line voltages, in magnitude, are √3 times the phase voltages, and the phase voltages lag the corresponding line voltages by 30°.

The phasor diagram is drawn in Figure(b), from which it can be observed that the balanced line (or phase) currents lag the corresponding line-to-neutral voltages by the impedance

55_Balanced Wye-Connected Load2.png

angle (20° in our example). The load power factor is given by cos 20° for our problem, and it is said to be lagging in this case, as the impedance angle is positive and the phase current lags the corresponding phase voltage by that angle.

The problem can also be solved in a simpler way by making use of a single-line equivalent circuit, as shown in Figure(c),

303_Balanced Wye-Connected Load3.png

in which ¯ VL-N is chosen as the reference for convenience. The magnitude of the line current and the power factor angle are known; the negative sign associated with the angle indicates that the power factor is lagging. By knowing that the line (or phase) currents ¯IA, ¯IB, ¯IC lag their respective voltages ¯VAN, ¯VBN, and ¯VCN by 20°, the phase angles of various voltages and currents, if desired, can be obtained with respect to any chosen reference, such as ¯VBC.


Related Discussions:- Explain balanced wye-connected load

Determine the armature e.m.f. and load angle of generator, A 3-phase, wye-c...

A 3-phase, wye-connected, 11 kV, 137.5 MVA turbo-alternator of 0.8 power factor lagging has a synchronous reactance XS = 1.4 Ω. Assume the machine to be ideal for convenience of an

Oscilloscope, Describe in detail the construction and working of digital ty...

Describe in detail the construction and working of digital type oscilloscope.

Operations on vectors, Can add vectors using the parallelogram rule Can ...

Can add vectors using the parallelogram rule Can multiply a vector by a scalar            - result is a parallel vector                        • length is scaled

What are the five stages in a dlx pipeline, The five stages of DLX pipeline...

The five stages of DLX pipeline is:- ? Operand location ? Number of explicit operands per instruction ? Operand storage in the CPU ? Operations ? Type and size of o

Find out the equivalent two-port amplifier model, Refer to the circuit show...

Refer to the circuit shown below containing a two-port network. The two-port is a transconductance amplifier. The input port of the two-port is defined by terminals A and B. T

Explain industry standard architecture bus, Explain the term Industry Stand...

Explain the term Industry Standard Architecture Bus. The Industry Standard Architecture, bus has been approximately since the very start of the IBM-compatible personal computer

Why we need digital systems, Q. Why we need digital systems? EASIER TO ...

Q. Why we need digital systems? EASIER TO PROCESS: For the reason that digitized information breaks all information into discrete units the information is easier to process and

Calculate the maximum length of an optical fibre, Calculate the maximum len...

Calculate the maximum length of an optical fibre that exhibits 0.8dB/km attenuation if the optical output is 10mW and the power launched at the input is 150mW. [Hint: Loss, L=10 lo

Flex routing , Flex Routing : You can see that your labour will have bee...

Flex Routing : You can see that your labour will have been in vain unless you take steps to ensure that flexes are routed safely and well clear of possible sources of danger.

Determine the current through each resistor, For the circuit of Fig 1a: ...

For the circuit of Fig 1a: (i) Using Ohm's Law , determine the equivalent resistance across the battery (ii)  determine the current through each resistor (iii) the arrang

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd