Explain balanced wye-connected load, Electrical Engineering

Assignment Help:

Balanced Wye-Connected Load

Let us consider a three-phase, four-wire 208-V supply system connected to a balanced wye connected load with an impedance of 10 20° , as shown in Figure (a). We shall solve for the line currents and draw the corresponding phasor diagram.

Conventionally it is assumed that 208 V is the rms value of the line-to-line voltage of the supply system, and the phase sequence is positive, or A-B-C, unless mentioned otherwise. The magnitude of the line-to-neutral (or phase) voltages is given by 208/√3, or 120 V. Selecting the line currents returning through the neutral conductor, as shown in Figure, we have

1407_Balanced Wye-Connected Load.png

Note that ¯VBC has been chosen arbitrarily as the reference phasor, as in Figure (b). Assuming the direction of the neutral current toward the load as positive, we obtain

1532_Balanced Wye-Connected Load1.png

That is to say that the system neutral and the star point of the wye-connected load are at the same potential, even if they are not connected together electrically. It makes no difference whether they are interconnected or not.

Thus, for a balanced wye-connected load, the neutral current is always zero. The line currents and phase currents are equal inmagnitude, and the line currents are in phasewith the corresponding phase currents. The line-to-line voltages, in magnitude, are √3 times the phase voltages, and the phase voltages lag the corresponding line voltages by 30°.

The phasor diagram is drawn in Figure(b), from which it can be observed that the balanced line (or phase) currents lag the corresponding line-to-neutral voltages by the impedance

55_Balanced Wye-Connected Load2.png

angle (20° in our example). The load power factor is given by cos 20° for our problem, and it is said to be lagging in this case, as the impedance angle is positive and the phase current lags the corresponding phase voltage by that angle.

The problem can also be solved in a simpler way by making use of a single-line equivalent circuit, as shown in Figure(c),

303_Balanced Wye-Connected Load3.png

in which ¯ VL-N is chosen as the reference for convenience. The magnitude of the line current and the power factor angle are known; the negative sign associated with the angle indicates that the power factor is lagging. By knowing that the line (or phase) currents ¯IA, ¯IB, ¯IC lag their respective voltages ¯VAN, ¯VBN, and ¯VCN by 20°, the phase angles of various voltages and currents, if desired, can be obtained with respect to any chosen reference, such as ¯VBC.


Related Discussions:- Explain balanced wye-connected load

Electronics, what is the difference between half &full wave rectifier

what is the difference between half &full wave rectifier

Determine the stations visual-carrier frequency, If a television station op...

If a television station operates on UHF channel 20 (band 506-512 MHz), determine the station's visual-carrier frequency.

Explain cold rolled grain oriented steel, Discuss the properties and uses o...

Discuss the properties and uses of Cold rolled grain oriented steel. Cold rolled grain oriented steel:  Grain orientation of silicon steel is acquired by a special technique

Memory address - address bus , Memory Address The memory  address is of...

Memory Address The memory  address is of 16  bits. It ranges from 0000?H to  FFFH 16bits address lines of 8085 microprocessor are  capable  of addressing 216 i e 65, 536, ( or

Obtain the sop expression, Q. Given the K map of a logic function as shown ...

Q. Given the K map of a logic function as shown in Figure, in which ds denote don't-care conditions, obtain the SOP expression.

Critical rate of rise of current - thyristor , Critical Rate of  Rise of ...

Critical Rate of  Rise of Current The maximum  rate of  increase of current  during  on state  which  the SCR  can tolerate is called  the critical rate of rise  of current  f

If a single phase motor fails to run, Q. If a single phase motor fails to r...

Q. If a single phase motor fails to run or start slow what action to be taken. Ans: If it is not starting check the supply and test the winding if it found normal check

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd