Balanced Wye-Connected Load

Let us consider a three-phase, four-wire 208-V supply system connected to a balanced wye connected load with an impedance of 10 20° , as shown in Figure (a). We shall solve for the line currents and draw the corresponding phasor diagram.

Conventionally it is assumed that 208 V is the rms value of the line-to-line voltage of the supply system, and the phase sequence is positive, or A-B-C, unless mentioned otherwise. The magnitude of the line-to-neutral (or phase) voltages is given by 208/√3, or 120 V. Selecting the line currents returning through the neutral conductor, as shown in Figure, we have

1407_Balanced Wye-Connected Load.png

Note that ¯VBC has been chosen arbitrarily as the reference phasor, as in Figure (b). Assuming the direction of the neutral current toward the load as positive, we obtain

1532_Balanced Wye-Connected Load1.png

That is to say that the system neutral and the star point of the wye-connected load are at the same potential, even if they are not connected together electrically. It makes no difference whether they are interconnected or not.

Thus, for a balanced wye-connected load, the neutral current is always zero. The line currents and phase currents are equal inmagnitude, and the line currents are in phasewith the corresponding phase currents. The line-to-line voltages, in magnitude, are √3 times the phase voltages, and the phase voltages lag the corresponding line voltages by 30°.

The phasor diagram is drawn in Figure(b), from which it can be observed that the balanced line (or phase) currents lag the corresponding line-to-neutral voltages by the impedance

55_Balanced Wye-Connected Load2.png

angle (20° in our example). The load power factor is given by cos 20° for our problem, and it is said to be lagging in this case, as the impedance angle is positive and the phase current lags the corresponding phase voltage by that angle.

The problem can also be solved in a simpler way by making use of a single-line equivalent circuit, as shown in Figure(c),

303_Balanced Wye-Connected Load3.png

in which ¯ VL-N is chosen as the reference for convenience. The magnitude of the line current and the power factor angle are known; the negative sign associated with the angle indicates that the power factor is lagging. By knowing that the line (or phase) currents ¯IA, ¯IB, ¯IC lag their respective voltages ¯VAN, ¯VBN, and ¯VCN by 20°, the phase angles of various voltages and currents, if desired, can be obtained with respect to any chosen reference, such as ¯VBC.


Related Discussions:- Explain balanced wye-connected load

State faraday''s law, Faraday's Law Faraday's laws of electromagnetic i...

Faraday's Law Faraday's laws of electromagnetic induction state: i)  An induced e.m.f is setup when the magnetic field linking that circuit changes ii)  The magnitude of

The filter capacitor , It is needed to use a half-wave rectifier for a dc p...

It is needed to use a half-wave rectifier for a dc power supply that gives an average dc output voltage of 15 V and a maximum ±1V ripple is permitted. The rectifier feeds a load of

Analysis on solar charging system buck converter with VMC, PLS WRITE THE IN...

PLS WRITE THE INTRODUCTION, METHODOLOGY AND LITERATURE REVIEW

Thermal considerations, Thermal considerations: At continuous current,...

Thermal considerations: At continuous current, the voltage across the emitter-base junction V BE of a bipolar transistor get decreases 2 mV (silicon) and 1.8mV (germanium) fo

Machine, function of a commutator in a DC motor

function of a commutator in a DC motor

Sampled-data and digital control systems, Q. Sampled-data and digital contr...

Q. Sampled-data and digital control systems? These differ fromthe continuous-data systems in that the signals at one or more points of the system are in the form of either a pu

Circuit with inductive load, Circuit with inductive load  Electromagnet...

Circuit with inductive load  Electromagnetic induction When a conductor is moved across a magnetic field so as to cut by the lines of force (or flux, an electromotive force

Any number system to decimal conversion , Any number System  to Decimal Co...

Any number System  to Decimal Conversion To convert a number in any number system to its  equivalent  decimal number, simply multiple each  digit of the number  with its  posi

Describe common-mode rejection ratio, Q. Describe Common-Mode Rejection Rat...

Q. Describe Common-Mode Rejection Ratio ? When there is a common-mode input voltage, i.e., when the input signals are equal and greater than zero, the output voltage of an idea

Derive the transfer function, A data hold is to be constructed that reconst...

A data hold is to be constructed that reconstructs the sampled signal by the straight-line approximation shown in Figure. Note that this device is a polygonal data hold with a dela

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd