Explain balanced wye-connected load, Electrical Engineering

Assignment Help:

Balanced Wye-Connected Load

Let us consider a three-phase, four-wire 208-V supply system connected to a balanced wye connected load with an impedance of 10 20° , as shown in Figure (a). We shall solve for the line currents and draw the corresponding phasor diagram.

Conventionally it is assumed that 208 V is the rms value of the line-to-line voltage of the supply system, and the phase sequence is positive, or A-B-C, unless mentioned otherwise. The magnitude of the line-to-neutral (or phase) voltages is given by 208/√3, or 120 V. Selecting the line currents returning through the neutral conductor, as shown in Figure, we have

1407_Balanced Wye-Connected Load.png

Note that ¯VBC has been chosen arbitrarily as the reference phasor, as in Figure (b). Assuming the direction of the neutral current toward the load as positive, we obtain

1532_Balanced Wye-Connected Load1.png

That is to say that the system neutral and the star point of the wye-connected load are at the same potential, even if they are not connected together electrically. It makes no difference whether they are interconnected or not.

Thus, for a balanced wye-connected load, the neutral current is always zero. The line currents and phase currents are equal inmagnitude, and the line currents are in phasewith the corresponding phase currents. The line-to-line voltages, in magnitude, are √3 times the phase voltages, and the phase voltages lag the corresponding line voltages by 30°.

The phasor diagram is drawn in Figure(b), from which it can be observed that the balanced line (or phase) currents lag the corresponding line-to-neutral voltages by the impedance

55_Balanced Wye-Connected Load2.png

angle (20° in our example). The load power factor is given by cos 20° for our problem, and it is said to be lagging in this case, as the impedance angle is positive and the phase current lags the corresponding phase voltage by that angle.

The problem can also be solved in a simpler way by making use of a single-line equivalent circuit, as shown in Figure(c),

303_Balanced Wye-Connected Load3.png

in which ¯ VL-N is chosen as the reference for convenience. The magnitude of the line current and the power factor angle are known; the negative sign associated with the angle indicates that the power factor is lagging. By knowing that the line (or phase) currents ¯IA, ¯IB, ¯IC lag their respective voltages ¯VAN, ¯VBN, and ¯VCN by 20°, the phase angles of various voltages and currents, if desired, can be obtained with respect to any chosen reference, such as ¯VBC.


Related Discussions:- Explain balanced wye-connected load

Determine line voltage for the y- connected machine, A 3-phase, 16-pole syn...

A 3-phase, 16-pole synchronous machine is driven by a prime mover at a speed of 600-rpm with the stator open circuited. The rotor flux per pole is 0.025-Wb. Determine (a) the fr

Determine the peak fundamental component of the mmf, Q. A two-pole, three-p...

Q. A two-pole, three-phase synchronous generator has a balanced three-phase winding with 15 turns per phase. If the three-phase currents are given by i a = 100 cos 377t, i b =

Determine the node voltage by using kcl, Determine the node voltage by usin...

Determine the node voltage by using KCL: Determine the node voltage V and then current flowing through each element by using KCL. Solution Apply KCL at the node whose

Forth generation, Forth Generation VLSI  technology  of IC made it poss...

Forth Generation VLSI  technology  of IC made it possible  to design the  complete  circuit  of ALU  Arithmetic  logic unit and cu ( Control Unit ) within  single  chip  which

Explain about simplex communication, Q. Explain about Simplex communication...

Q. Explain about Simplex communication? Simplex communication: Microphone and the earphone are transducer elements of the telephone communication system. Microphone converts

Transmission of electricity, explain all the components involved in transmi...

explain all the components involved in transmission of electricity

Transformers, Three transformers are provided with the following rating val...

Three transformers are provided with the following rating values: 1) 2400/240 V, 55kVA, Req1 = (0.1 + 0.0Y) Ohm and Xeq1 = (0.15 + 0.XX) Ohm. 2) 240/120 V, 25kVA, Req1 = (0.1

Drawing, #question what are the types of lines used there and their applica...

#question what are the types of lines used there and their application ..

8 bit data to memory - move immediate instruction , 8 bit  data to memory ...

8 bit  data to memory This form  of the  instruction is used to  copy 8 bit  data directly  to the memory  location pointed  by register pair HL.  The instruction  format is

Essay, Transmission parameters are more effective than the hybrid parameter...

Transmission parameters are more effective than the hybrid parameters for simulation of the transmission line

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd