Explain balanced wye-connected load, Electrical Engineering

Assignment Help:

Balanced Wye-Connected Load

Let us consider a three-phase, four-wire 208-V supply system connected to a balanced wye connected load with an impedance of 10 20° , as shown in Figure (a). We shall solve for the line currents and draw the corresponding phasor diagram.

Conventionally it is assumed that 208 V is the rms value of the line-to-line voltage of the supply system, and the phase sequence is positive, or A-B-C, unless mentioned otherwise. The magnitude of the line-to-neutral (or phase) voltages is given by 208/√3, or 120 V. Selecting the line currents returning through the neutral conductor, as shown in Figure, we have

1407_Balanced Wye-Connected Load.png

Note that ¯VBC has been chosen arbitrarily as the reference phasor, as in Figure (b). Assuming the direction of the neutral current toward the load as positive, we obtain

1532_Balanced Wye-Connected Load1.png

That is to say that the system neutral and the star point of the wye-connected load are at the same potential, even if they are not connected together electrically. It makes no difference whether they are interconnected or not.

Thus, for a balanced wye-connected load, the neutral current is always zero. The line currents and phase currents are equal inmagnitude, and the line currents are in phasewith the corresponding phase currents. The line-to-line voltages, in magnitude, are √3 times the phase voltages, and the phase voltages lag the corresponding line voltages by 30°.

The phasor diagram is drawn in Figure(b), from which it can be observed that the balanced line (or phase) currents lag the corresponding line-to-neutral voltages by the impedance

55_Balanced Wye-Connected Load2.png

angle (20° in our example). The load power factor is given by cos 20° for our problem, and it is said to be lagging in this case, as the impedance angle is positive and the phase current lags the corresponding phase voltage by that angle.

The problem can also be solved in a simpler way by making use of a single-line equivalent circuit, as shown in Figure(c),

303_Balanced Wye-Connected Load3.png

in which ¯ VL-N is chosen as the reference for convenience. The magnitude of the line current and the power factor angle are known; the negative sign associated with the angle indicates that the power factor is lagging. By knowing that the line (or phase) currents ¯IA, ¯IB, ¯IC lag their respective voltages ¯VAN, ¯VBN, and ¯VCN by 20°, the phase angles of various voltages and currents, if desired, can be obtained with respect to any chosen reference, such as ¯VBC.


Related Discussions:- Explain balanced wye-connected load

Phisics, deriving formula of the frictional force

deriving formula of the frictional force

Calculate the maximum power that transmitted to the load, Calculate the Max...

Calculate the Maximum Power That Transmitted To the Load? A 25 MW load at the 33 kV receiving-end busbar of a short 3-phase transmission line has a power factor of 0.8 lagging.

Laws of magnetic induction, The observations from these experiments led to ...

The observations from these experiments led to 'The Laws of Electromagnetic Induction' 1)  'If the magnetic flux threading through an electrical circuit changes, then an e.m.f.

Need for modulation recognition - software defined radio, Need for Modulati...

Need for Modulation Recognition There are so many communication signals all available with different types of modulation and different frequencies. It is necessary to identify

The time constant of the field winding, The field winding of a 200 V d.c. m...

The field winding of a 200 V d.c. machine has a resistance of 20? and an inductance of 500mH. Calculate: (a)  The time constant of the field winding (b)  The value of curr

What do you understand by analog to digital conversion, Q. What do you unde...

Q. What do you understand by Analog to Digital conversion? What do you understand by A/D conversion? Give an explanation of any one of the following A/D techniques: (i) Su

Determine the all-day efficiency, Q. A transformer has its maximum efficien...

Q. A transformer has its maximum efficiency of 0.9800 when it delivers 15 kVA at unity power factor. During the day it is loaded as follows: 12 hours 2 kW at power factor 0.5

Electonic principles, can you help with my electronic principle assignment

can you help with my electronic principle assignment

Give the basic structure of a basic dma module, a) Give four features that ...

a) Give four features that were traditionally reserved to RISC architectures? b) Determine the overall throughput for 21 sequential instructions assuming a four-stage pipeline a

What do you mean by sign bit, Q. What do you mean by Sign Bit? The sign...

Q. What do you mean by Sign Bit? The sign bit is like simple as it gets 0 denotes a positive number and 1 denote a negative number and flipping the value of this bit flips the

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd