Explain balanced wye-connected load, Electrical Engineering

Assignment Help:

Balanced Wye-Connected Load

Let us consider a three-phase, four-wire 208-V supply system connected to a balanced wye connected load with an impedance of 10 20° , as shown in Figure (a). We shall solve for the line currents and draw the corresponding phasor diagram.

Conventionally it is assumed that 208 V is the rms value of the line-to-line voltage of the supply system, and the phase sequence is positive, or A-B-C, unless mentioned otherwise. The magnitude of the line-to-neutral (or phase) voltages is given by 208/√3, or 120 V. Selecting the line currents returning through the neutral conductor, as shown in Figure, we have

1407_Balanced Wye-Connected Load.png

Note that ¯VBC has been chosen arbitrarily as the reference phasor, as in Figure (b). Assuming the direction of the neutral current toward the load as positive, we obtain

1532_Balanced Wye-Connected Load1.png

That is to say that the system neutral and the star point of the wye-connected load are at the same potential, even if they are not connected together electrically. It makes no difference whether they are interconnected or not.

Thus, for a balanced wye-connected load, the neutral current is always zero. The line currents and phase currents are equal inmagnitude, and the line currents are in phasewith the corresponding phase currents. The line-to-line voltages, in magnitude, are √3 times the phase voltages, and the phase voltages lag the corresponding line voltages by 30°.

The phasor diagram is drawn in Figure(b), from which it can be observed that the balanced line (or phase) currents lag the corresponding line-to-neutral voltages by the impedance

55_Balanced Wye-Connected Load2.png

angle (20° in our example). The load power factor is given by cos 20° for our problem, and it is said to be lagging in this case, as the impedance angle is positive and the phase current lags the corresponding phase voltage by that angle.

The problem can also be solved in a simpler way by making use of a single-line equivalent circuit, as shown in Figure(c),

303_Balanced Wye-Connected Load3.png

in which ¯ VL-N is chosen as the reference for convenience. The magnitude of the line current and the power factor angle are known; the negative sign associated with the angle indicates that the power factor is lagging. By knowing that the line (or phase) currents ¯IA, ¯IB, ¯IC lag their respective voltages ¯VAN, ¯VBN, and ¯VCN by 20°, the phase angles of various voltages and currents, if desired, can be obtained with respect to any chosen reference, such as ¯VBC.


Related Discussions:- Explain balanced wye-connected load

Calculate maximum reactive power the generator can produce, A 3-phase, wye-...

A 3-phase, wye-connected, 11.8 kV, 100 MVA turbo- generator of 0.8 power factor lagging has a synchronous reactance of 2.0 p.u. on rating. The generator is driven by a steam turbin

Explain digital control systems, Q. Explain Digital control systems? Si...

Q. Explain Digital control systems? Significant progress has been made in recent years in discrete-data and digital control systems because of the advancesmade in digital compu

Effect of feedback on sensitivity to parameter changes, Q. Effect of feedba...

Q. Effect of feedback on sensitivity to parameter changes? A good control system, in general, should be rather insensitive to parameter variations, while it is still able to fo

Explain the configuration of a step-by-step switching system, With neat dia...

With neat diagrams explain the configuration of a step-by-step switching system. Schematic diagram for such an exchange is given in Figure.  Every subscriber is connected to a

Find in wavelengths how long the line, Q. A transmission line with air diel...

Q. A transmission line with air dielectric is 25 m long. Find, in wavelengths, how long the line is at frequencies of 1 kHz, 10 MHz, and 100 MHz.

Amplifiers, what is the use of capacitors in amplifiers

what is the use of capacitors in amplifiers

Explain the johnson counters, Explain the Johnson Counters? The Johnson...

Explain the Johnson Counters? The Johnson counters are a variation of standard ring counters with the inverted output of the last stage fed back to the input of the first stage

Circuit of a common drain fet amplifier and explain, Q. Draw the circuit of...

Q. Draw the circuit of a common drain FET amplifier and explain. FET amplifier circuit The weak signal is applied between gate and source and amplified output is obtained

Write a short note on rs-232-c, Write a short note on RS-232-C. The RS-...

Write a short note on RS-232-C. The RS-232 standard is a collection of connection standards among different pieces of equipment. The EIA RS-232 serial communication standard is

Working of a sweep frequency generator, Q. With suitable diagram explains t...

Q. With suitable diagram explains the working of a sweep frequency generator. Sol. A sweep frequency generator or sweeper is a special type of signal generator in which the o

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd