Example numerical of dc generator., Electrical Engineering

Assignment Help:

Q. An 8 - pole dc generator has 500 armature conductors and has a useful flux per pole of 0.065 web. What will be the emf generated if it is lap connected and runs at 1000 r.p.m.  What must be the speed at which it is to be driven to produce the same emf if it is wave wound?  

Ans.

E1   = N1PΦZ/60A = 10000 × 0.065 ×500 ×  P/A

               For lap connection A = P

 

                       E1  =  10000 × 0.065 ×500 /60 = 541.67 volts

 

                       E2  = N28ΦZ/60 × 2

 

 Since                  E2  = E1

 

                             8N2ΦZ/60 × 2 = 8N1ΦZ/60 × 8

 

                       N2 = N1 × 2/8 = 1000 × 2/8 = 250 rpm


Related Discussions:- Example numerical of dc generator.

Can you explain working principle of tl - ac alternator, Can you explain wo...

Can you explain working principle of TL/AC alternator? Ans . The core of the stator which is completely induced by the field coils, will get a residual magnetism if excited b

Case 2 a>b - program description, Case 2 ( A>B) Suppose XX = 05H ( stor...

Case 2 ( A>B) Suppose XX = 05H ( stored  in A ) And  YY = 02H ( stored  in B). Then carry  flag will  reset by CMP instruction, since  A> B in this  case JNC  will transfer the

Find the ratio of the speed of the generator, Q. A dc shunt machine has an ...

Q. A dc shunt machine has an armature winding resistance of 0.12  and a shunt-?eld winding resistance of 50 . The machine may be run on 250-V mains as either a generator or a mot

Substations, How to calculate Electrical losses by transformation

How to calculate Electrical losses by transformation

Discrete time system transfer function, For a discrete time unit step input...

For a discrete time unit step input x(kT), the output  y(kT) of a system is shown below,   Part (a)  Obtain the Z-transform of the output signal y(kT).   Part (b)   F

Complex waveforms and transients in rlc circuits, can you let me know how m...

can you let me know how much it would be for the answer to a question that has 2 parts

Connection of shunt capacitors - across individual customers, Connection of...

Connection of Shunt Capacitors - Across Individual Customers The most appropriate manner of improving PF of the distribution system and thereby reducing line losses is to link

Second generation 1954- 1964- history of computer , Second Generation ( 195...

Second Generation ( 1954- 1964) After the invention of semiconductor devices mainly transistors size of computer s was reduced a lot computing power increased reliability was

Utilization of electrical energy, Ask question #Discuss the role of load fa...

Ask question #Discuss the role of load factor on the cost of electrical energy 100 words accepted#

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd