Determine the shaft power output:

A 6-pole, 50 Hz, 3-phase induction motor running on full load develops a useful torque of 180 Nm when the rotor emf frequency is 2 Hz. Determine the shaft power output. If the mechanical torque lost in friction and that for core-loss is 12 Nm, determine

(a) the input to the motor, and

(b) efficiency.

The total stator loss is 900 W.

Solution

f2  = S f  = 2

S =  2 /50 = 0.04

N s   = (120 × 50 )/6= 1000 RPM

Nr  = (1 - S ) N s  = (1 - 0.04) 1000 = 960 RPM

ω r = (2 π× 960 )/60 = 100.53 rad/s

Shaft power output = 180 × 100.53 = 18.095 kW

Mechanical power developed = (180 + 12) × 100.53 = 19.301 kW

P m   = Rotor copper loss ( (1/S) - 1)

Rotor copper loss = Pm (S/(1-S) = 19.301 (0.04/(1-0.04) = 0.804 kW

(a) Input to the motor = 19.301 + 0.804 + 0.9 = 21.005 kW

(b) Efficiency of motor = 18.095 × 100 = 86.14%


Related Discussions:- Determine the shaft power output

Explain index mode and base address mode, Explain index mode and base addre...

Explain index mode and base address mode (with examples) available in microprocessors. Index Mode and Base Address Mode: Address supplied through the instruction is adde

Compute the firing angle for the rated braking torque, Consider a 3-hp, 220...

Consider a 3-hp, 220-V, 1800-r/min separately excited dcmotor controlled by a single-phase fully controlled rectifierwith an ac source voltage of 230Vat 60Hz.Assume that the full-l

Explain the working of a single stage rc coupled amplifier, Q. Diagram, exp...

Q. Diagram, explain the construction of a single stage RC coupled amplifier? An RC Coupled amplifier consists of a transistor connected in the emitter configuration with neces

How address and data lines are demultiplexed in 8085, How address and data ...

How address and data lines are demultiplexed in 8085? AD0-AD7 lines are multiplexed and the lower half of address A0-A7 is available only during T1  of the machine cycle. This

Explain current-to-current amplifier, Q. Explain Current-to-Current Amplifi...

Q. Explain Current-to-Current Amplifier ? The circuit given in Figure is to amplify a current fed to the input of the op amp. Applying KCL at Y, i 1 + i S = i o S

Cro, explain the operation of a detector probe

explain the operation of a detector probe

Power machines., name two types of axial flow turbines

name two types of axial flow turbines

Gto - gate turn off, GTO ( Gate Turn Off) GTO stands for gate  turn o...

GTO ( Gate Turn Off) GTO stands for gate  turn off  thyristor . it is four layer  PNPN  device. It can be  triggered into conduction like a conventional thyristor  by a pulse

Dc machines, a 400V 4-pole DC generator takes an armature current of 50A wh...

a 400V 4-pole DC generator takes an armature current of 50A when rotating at 626 rpm. the armature circuit resistance is 0,25ohms. determine the generated emf. DOC

Determine the required voltage at the high-voltage terminals, Q. A 20-kVA, ...

Q. A 20-kVA, 2200:220-V, 60-Hz, single-phase transformer has these parameters: Resistance of the 2200-V winding R1 = 2.50  Resistance of the 220-V winding R2 = 0.03  Lea

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd