Determine the active - reactive and apparent power:
In the given circuit, determine the active, reactive and apparent power.
Figure
Solution
The inductive reactance, XL = 2π fL
= 2π × 60 × 0.2
= 75.408 Ω
Impedance, Z = 15 + j 75.408 Ω
In polar form = 76.885 ∠ 78.749o Ω
Current in the Circuit
i = v/ Z = 220 ∠ 0o / 76.885 ∠78.749o
= 2.861 ∠ - 78.749o Amp (lagging)
Power factor cos φ = cos 78.749o
= 0.195 (lag)
and sin φ = sin 78.749o = 0.98
Active Power
P = VI cos φ
= 220 × 2.861 × 0.195
= 122.7 Watts
or P = I 2 R
Reactive Power
Q = VI sin φ
= 220 × 2.861 × 0.98
= 616.83 volt-Amp reactive or
Q = I 2 X
= 617.1 VA
Apparent Power
S = VI
= 220 × 2.861
= 629.42 Volt-amp
or
= 629.2 Volt-amp.
Q. Why FET is called a voltage-controlled device? Why its input resistance is high? In the case of a FET the output current ID is a function of the voltage VGS applied to the i
what is the contruction of a fixed capacitor
how emitter current equal to collector current
A 3-phase, wye-connected, 11.8 kV, 100 MVA turbo- generator of 0.8 power factor lagging has a synchronous reactance of 2.0 p.u. on rating. The generator is driven by a steam turbin
The Thevenin equivalent circuit at the terminals of R2 / S for a 60 hz, 6 pole induction motor is shown below. a) Find the value of the slip for maximum torque and the maximum t
Classify plastic materials into two categories describe their important properties and give two examples of each. Plastic materials can be categorized in thermoplastic and ther
what is crossmagnetisation in dc generator
I want simulink model for carrier based pwm method
Q. Explain the working principle of a Q meter. Also explain the factors that cause errors during a Q factor measurement. Ans. Working Principle of Q Meter: the q meter is
Q. Two three-phase generators are supplying to a common balanced three-phase load of 30 kW at 0.8 power factor lagging. The per-phase impedance of the lines connecting the generato
Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!
whatsapp: +1-415-670-9521
Phone: +1-415-670-9521
Email: [email protected]
All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd