Determine phase - voltage and power:
A balanced star connected load is supplied from a symmetrical 3-phase 440 Volt system. The current in each of the phase is 40 Amp and lags 30o behind the phase voltage. Determine
1. phase voltage,
2. power,
3. reactive power drawn by a the load, and
4. phase impedance.
Solution
For three phase star connected load voltage applied VL = 440 Volt
(a) V ph = 440/ √3 = 254.03 Volt
Power current = I ph = 40 ∠ - 30o Amp = I L
(b) Power P3φ =3 VL I L cos φ = 3 × 440 × 40 cos 30o
= 26400 Watt = 26.4 kW
(c) Reactive power drawn by the load:
Q3φ = √3 VL I L sin φ
= √3 × 440 × 40 sin 30o
= 15242.047 Var = 15.24 kVAr
(e) Phase impedance Z ph = V ph I ph
=254.03 ∠ 0o / 40 ∠- 30o = 6.35 ∠ 30o Ω
What is the size of ports in 8255? Port-A : 8-bits Port-CU : 4-bits Port-B : 8-bits Port-CL : 4-bits
a. Determine the power flow diagram for a DC generator. b. A shunt wound DC generator delivers 496 A at 440 V to a load. The resistance of the shunt field coil is 110? and that
Machine Control Instructions Instructions used to control various machine operations are kept in this group.
what is the equation for rc phase shift oscillator?
Q. Illustrate the Simplex Transmission? Simplex Transmission Data in a simplex channel is always one way. Simplex channels aren't often used as it is not possible to send ba
Q. Can you explain Twos complement addition? 2's Complement Addition Two's complement addition follows the same rules as binary addition. For example, 5 + (-3) = 2
to get PV curve i want optimal power flow program in matlab
Magnetic circuits To see how this is used in practice, consider a coil of N turns wound onto a closed ring shaped former with a very high (note: r (steel) = 200
Switching Characteristics Switching characteristics of BJT are shown in figure. Due to the presence of internal capacitances BJT cannot be turned instantly. Initially
An electromechanical voltmeter with internal resistance of 1 k and an electronic voltmeter with internal resistance of 10 M are used separately to measure the potential differenc
Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!
whatsapp: +91-977-207-8620
Phone: +91-977-207-8620
Email: [email protected]
All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd