Determine phase - voltage and power:
A balanced star connected load is supplied from a symmetrical 3-phase 440 Volt system. The current in each of the phase is 40 Amp and lags 30o behind the phase voltage. Determine
1. phase voltage,
2. power,
3. reactive power drawn by a the load, and
4. phase impedance.
Solution
For three phase star connected load voltage applied VL = 440 Volt
(a) V ph = 440/ √3 = 254.03 Volt
Power current = I ph = 40 ∠ - 30o Amp = I L
(b) Power P3φ =3 VL I L cos φ = 3 × 440 × 40 cos 30o
= 26400 Watt = 26.4 kW
(c) Reactive power drawn by the load:
Q3φ = √3 VL I L sin φ
= √3 × 440 × 40 sin 30o
= 15242.047 Var = 15.24 kVAr
(e) Phase impedance Z ph = V ph I ph
=254.03 ∠ 0o / 40 ∠- 30o = 6.35 ∠ 30o Ω
a 400V 4-pole DC generator takes an armature current of 50A when rotating at 626 rpm. the armature circuit resistance is 0,25ohms. determine the generated emf. DOC
Normal 0 false false false EN-IN X-NONE X-NONE Induction Heating When alternating curren
Q. A two-pole, three-phase synchronous generator has a balanced three-phase winding with 15 turns per phase. If the three-phase currents are given by i a = 100 cos 377t, i b =
Q. What are the Display Devices? Display devices can be categorized as on/off indicators, numeric, alphanumeric, or graphical displays. They may also be classified as active an
Q. For the circuit of Figure: (a) Find an expression for the power absorbed by the load as a function of RL. (b) Plot the power dissipated by the load as a function of the lo
Q. A shunt generator gives full load output of 30 kW at a terminal voltage of 200V. The armature and field resistance are 0.05? and 50? resp.. The iron and friction losses are 10
Q. What do you understand by major systems of a telecommunication network? Explain in detail the subscriber loop systems. Ans: Major systems of any telecommunication netw
Switching Characteristics Switching characteristics are also know as dynamic or transient characteristics these characteristics give the information about the time varia
Explain iron and silicon iron alloys. Iron: Galvanised steel and iron wires that are usually used for earth conductor in low voltage distribution systems may also be utilize
Usage: Because of the above inherent drawbacks, fixed bias is seldom used in linear circuits (that is those circuits which use the transistor like a current source). Instead,
Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!
whatsapp: +91-977-207-8620
Phone: +91-977-207-8620
Email: [email protected]
All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd