Determine phase - voltage and power, Electrical Engineering

Assignment Help:

Determine phase - voltage and power:

A balanced star connected load is supplied from a symmetrical 3-phase 440 Volt system. The current in each of the phase is 40 Amp and lags 30o behind the phase voltage. Determine

1.      phase voltage,

2.      power,

3.      reactive power drawn by a the load, and

4.      phase impedance.

Solution

For three phase star connected load voltage applied VL = 440 Volt

(a)                  V ph    = 440/ √3 = 254.03 Volt

Power current = I ph = 40 ∠ - 30o Amp = I L

 (b)       Power P =3 VL I L cos φ   = 3 × 440 × 40 cos 30o

                                                            = 26400 Watt = 26.4 kW

(c)        Reactive power drawn by the load:

Q= √3 VL I L sin φ

= √3 × 440 × 40 sin 30o

= 15242.047 Var = 15.24 kVAr

 (e)       Phase impedance Z ph = V ph I ph

               =254.03 ∠ 0o / 40 ∠- 30o = 6.35 ∠ 30o Ω


Related Discussions:- Determine phase - voltage and power

Principles for implementation of strategy in organization, Principles for I...

Principles for Implementation of Strategy in an Organization Organization required focusing on five principles for the successful implementation of strategy. Organizations wil

Calculate the voltage regulation, The per-phase synchronous reactance of a ...

The per-phase synchronous reactance of a three-phase, wye-connected, 2.5-MVA, 6.6-kV, 60-Hz turboalternator is 10 . Neglect the armature resistance and saturation. Calculate the v

Write a short note dispersion shifted dispersion flat fiber, Write a short ...

Write a short note on dispersion shifted and dispersion flatted fibers? The dispersion features of a fiber is display below: The overall dispersion is the sum of materi

Energy, Explain different stage in energy audit?

Explain different stage in energy audit?

Discuss the characteristics of embedded systems, Problem : a) What is a...

Problem : a) What is an "Embedded System"? Discuss the characteristics of Embedded Systems. b) Describe three downfalls of "Embedded Systems". c) Explain the difference b

Determine the dimensions of the new model, The manufacturers of the tank de...

The manufacturers of the tank described in Problem would like to  design another model, with twice the capacity of the one described in figure. The ratio of height to diameter must

3-phase bridge inverter, 3-phase  Bridge Inverter In 3-phase bridge in...

3-phase  Bridge Inverter In 3-phase bridge inverter six thyristors an six diodes are used as shown in figure  a capacitor at input terminal is connected so that the input volta

Determine phase - voltage and power, Determine phase - voltage and power: ...

Determine phase - voltage and power: A balanced star connected load is supplied from a symmetrical 3-phase 440 Volt system. The current in each of the phase is 40 Amp and lags

Electricity, Describe the nature of electricity

Describe the nature of electricity

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd