Determine phase - voltage and power:
A balanced star connected load is supplied from a symmetrical 3-phase 440 Volt system. The current in each of the phase is 40 Amp and lags 30o behind the phase voltage. Determine
1. phase voltage,
2. power,
3. reactive power drawn by a the load, and
4. phase impedance.
Solution
For three phase star connected load voltage applied VL = 440 Volt
(a) V ph = 440/ √3 = 254.03 Volt
Power current = I ph = 40 ∠ - 30o Amp = I L
(b) Power P3φ =3 VL I L cos φ = 3 × 440 × 40 cos 30o
= 26400 Watt = 26.4 kW
(c) Reactive power drawn by the load:
Q3φ = √3 VL I L sin φ
= √3 × 440 × 40 sin 30o
= 15242.047 Var = 15.24 kVAr
(e) Phase impedance Z ph = V ph I ph
=254.03 ∠ 0o / 40 ∠- 30o = 6.35 ∠ 30o Ω
What are the basic components in a Microprocessor? 1) Address lines to refer to the address of a block 2) Data lines for data transmit 3) IC chips 4 processing data
A 500 MVA, 33kv, three phase steam turbine generator has a synchronous reactance of 1.6 p.u. It delivers a rated output at 0.8 power factor lagging. Calculate (a) The synchronou
Design a combinational logic circuit to convert XS3BCD code in to the standard 8421 BCD code.
how much and what to write it is of 30 marks
To demonstrate a practical method of testing semiconductor diodes.
What are the advantages of distributing windings in an alternator?
Write short notes of the following. a) Microprocessor b) Modes of data transfer. c) I/O processor d) Associative memory e) Software and Hardware interrupt
What is polarisation? Explain. While a dielectric material is related an electric field the dipoles of the material find oriented in a certain direction under the effect of the
Two single-phase 60-Hz sinusoidal-source generators (with negligible internal impedances) are supplying to a common load of 10 kW at 0.8 power factor lagging. The impedance of the
How do i calculate critical resistance?
Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!
whatsapp: +91-977-207-8620
Phone: +91-977-207-8620
Email: [email protected]
All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd