Determine phase - voltage and power:
A balanced star connected load is supplied from a symmetrical 3-phase 440 Volt system. The current in each of the phase is 40 Amp and lags 30o behind the phase voltage. Determine
1. phase voltage,
2. power,
3. reactive power drawn by a the load, and
4. phase impedance.
Solution
For three phase star connected load voltage applied VL = 440 Volt
(a) V ph = 440/ √3 = 254.03 Volt
Power current = I ph = 40 ∠ - 30o Amp = I L
(b) Power P3φ =3 VL I L cos φ = 3 × 440 × 40 cos 30o
= 26400 Watt = 26.4 kW
(c) Reactive power drawn by the load:
Q3φ = √3 VL I L sin φ
= √3 × 440 × 40 sin 30o
= 15242.047 Var = 15.24 kVAr
(e) Phase impedance Z ph = V ph I ph
=254.03 ∠ 0o / 40 ∠- 30o = 6.35 ∠ 30o Ω
Q. Show the procedure of Binary Addition? Rules of Binary Addition 0 + 0 = 0 0 + 1 = 1 1 + 0 = 1 1 + 1 = 0 , and carry 1 to the next more importan
Feedback amplifiers are of great importance in electronic circuits. The block diagram of a class of feedback amplifier is shown in Figure. Determine the transfer function C/R for t
There are many advantages of PLC a.The PLC was specifically designed for harsh conditions with electrical noise magnetic fields vibration extreme temperatures or humidit
How is 8255 (Programmable Peripheral Interface) configured if its control registercomprises 9B h. Ans 9BH => 1001 1011 => b6b5=00-> Mode0 b4=0-> Port A as
For the circuit of Figure(a), obtain the complete solution for the current i L (t) through the 5-H inductor and the voltage v x (t) across the 6- resistor.
Q. A two-winding, single-phase transformer rated 3 kVA, 220:110 V, 60 Hz is connected as an autotransformer to transform a line input voltage of 330 V to a line output voltage of 1
The distribution transformer is supplying a load at 240 V and 0.8 power factor lagging. The open-circuit and short-circuit test data are given in Example. (a) Determine the frac
write a short notes on hardness
Q. A synchronous motor operates continuously on the following duty cycle: 50 hp for 8 min, 100 hp for 8 min, 150 hp for 10 min, 120 hp for 20 min, and no load for 14min. Specify th
A 20µF capacitor is connected in series with a 50 kΩ resistor and the circuit is connected to a 20 V, d.c. supply. Verify: a) The initial value of the current flowing, b) T
Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!
whatsapp: +91-977-207-8620
Phone: +91-977-207-8620
Email: [email protected]
All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd