Determine Impedance in each branch - delta connection:
A delta connected balanced 3-phase load is supplied from a 3-phase 400 V supply. The line current is 30 Amp and the power taken by the load is 10 kW. Determine
1. impedance in each branch,
2. the phase current,
3. power factor, and
4. Power consumed if the same load is connected in star.
Solution
Delta Connection Load
Line current IL = 30 Amp
Phase current I ph = 30/√ 3 = 17.32 Amp
(a) Phase impedance Z ph = V ph / I ph = 400 V/17.32 Amp
= 23.095 Ω
(b) Phase current Iph = 30 Amp (already calculated)
(c) Total 3-phase power = 10 kW
But 3-phase power = √3 VL I L cos φ
∴ cos φ= P/ √3 VL I L = 10 × 1000 /√3 × 400 × 30
= 0.4811
(d) The same power shall be consumed if load is delta connected i.e. 10 kW.
Explain LOOP instructions in 8086 family with example and their effect on flag. LOOP: (Jump to given label until CX = 0) it is used to repeat a sequence of instructions for
Ask question #Minwhat is biasing of clamper imum 100 words accepted#
Q A high-pass filter circuit is shown in Figure. Using a PSpice program and PROBE, obtain the Bode magnitude plot for the transfer function ¯H(f) = ¯V out / ¯V in for frequency ra
Q. Two single-phase transformers, each rated 2400: 120-V, are to be interconnected for (a) 4800:240- V operation, and (b) 2400:120-V operation. Draw circuit diagrams and show polar
fdsf
Two projects using the principle of functional independence, increases system accuracy?
AskWrite short notes on pit head generation. question #Minimum 100 words accepted#
Now that you have the input and output impedances you can design the matching networks. I will require either the Smith Charts showing how you calculated the matching components or
Question : (a)(1) Show different types of voltmeters commonly used. (2) A basic d'Arsonval meter movement with an internal resistance Rm = 100 ?,and a full scale current of
Q. Illustrate Output-rate control? A system is said to have output-rate damping when the generation of the output quantity in some way ismade to depend upon the rate atwhich th
Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!
whatsapp: +1-415-670-9521
Phone: +1-415-670-9521
Email: [email protected]
All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd