Determine footing moment analysis, Mechanical Engineering

Assignment Help:

Determine footing moment analysis for given demonstration.

1648_Footing Moment Analysis.png

Ans:

Assuming effective depth as d, Bending moment M at the face of column

M = ((273.60 x 2.80 x (1.40 - 0.205)2)/2kN-m

= 547 kN-m = 547 x 106N.mm

d = (M/kb)1/2

Here K is obtained from exact formed table, L = 2800 rnm

d = (547 x 106)/(2.76 x 2800)

= 266 mm

You can see that in this particular example, one way shear controls the thickness of the footings. Effective depth of 530 mm is selected.


Related Discussions:- Determine footing moment analysis

Welding transformer, Welding transformer The resistance welding transfo...

Welding transformer The resistance welding transformers step down the line tune of 2 to 20 V. The primary is connected to the line supply and is made from edge bent copper stri

Belt drive, what is the equation which gives the relationship between the m...

what is the equation which gives the relationship between the maximum tension in the belt T1 and the centrifugal tension Tc if maximum power transmitted?

Isolated system - thermodynamics, Isolated System: In an Isolated syst...

Isolated System: In an Isolated system, neither energy nor masses are permitted to cross the boundary. The system has constant mass and energy. No such system exists physicall

Steam generator load balancing, Q. Steam Generator Load Balancing? The ...

Q. Steam Generator Load Balancing? The pressure controller output is cascaded to individual stations, one for each boiler. These allow selective increase or decrease of the du

What is a cotter joint, These parts of joints are used to connect two rods,...

These parts of joints are used to connect two rods, which are under compressive or tensile stress. The ends of the rods are in the manner of a socket and shaft that fit together an

#title., kinds of machine tempering

kinds of machine tempering

Ancillary railway structures, Ancillary Railway Structures: Overhe...

Ancillary Railway Structures: Overhead Transmission Lines When the line is electrified, the electric loco has to pick up the electric current from a cable that runs

Simply supported beam, Select a standard rolled steel I-section for the sim...

Select a standard rolled steel I-section for the simply supported beam shown in figure below. Select an appropriate factor of safety and material strength. Include references for

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd