Q. Design Pumps for plant layout?
Pumps handling flammable or combustible materials are relatively frequent sources of leakage and should therefore be located as far as practical from continuous ignition sources. They should not be located beneath other equipment, such as towers, drums, or pipe racks in order to avoid fire involvement of such equipment. Also, they should be located clear of overhead obstructions so they can be reached by a small crane. Where pumps are located within multi-level structures and portable crane access is not possible, monorails shall be installed for removal of the pump or internals during maintenance. A preferred location for pumps is on the opposite side of towers, away from fired heaters. In-line pumps should be treated the same as regular pumps for spacing purposes.
Hot pumps handling flammable materials present an increased fire risk because of the high likelihood of auto-ignition if a leak occurs. Pumps containing hydrocarbons operating above 316 °C (600 °F) or above its auto-ignition temperature (whichever is lower) should preferably not be located under or within multi-level structures. If unavoidable, fire protection measures such as passive fire protection or water sprays are required for equipment and structures above the pumps. However, the best choice is not to locate such pumps under or within structures.
Spacing separates pumps with higher fire potential and provides access for fire fighting. When a pump and its spare are exposed to a common fire hazard, additional separation between them may be justified to minimize the risk of losing both of them during a fire.
Pumps at grade should have prepared foundations with a paved area sloped to take spillage away from the pumps. Where pumps are required to be located in a structure, drip trays and anti-vibration mountings should be considered. For severe weather protection or noise reduction purposes some exposed pumps in critical service may be located in an enclosed or semi-enclosed shelter. In off-site areas, pumps should be grouped together outside the tank bermed areas.
What are the points that should be kept in mind during forging design? Some of the points which must be followed while forging design are: > A radial flow of fibers or grain
In case of welded vessels why is stress relieving in the form of post-weld treatment necessary? When a metal is welded together the point at which two surfaces are joined are s
hydraulic equipment metal tube stream map
Explain the Tool Signature The tool angles have been standardized by the American standards association. The seven important elements comprise the signature of the cutting tool
Derive the characteristic equations of motion for the underdamped, critical damped and overdamped free damped vibration system. Write short notes on i. Fourier series and har
What is fluid mechanics? what are cohesive and adhesive forces?
Shop assembled, steam drum, risers, downcomers, and all other related equipment on the steam side shall be designed, fabricated and hydrostatically tested to all requirements of AS
A cantilever beam of 1800 mm length is subjected to point loads of 3.5 kN, 4.3 kN, 1.2 kN and 2.8 kN at distances of 400 m, 400 m, 400 m 300 m and 300 m, respectively from the fixe
Question 1: Retail design tends to be rapid turnover business. Your potential client needs a window display for his retail sports wear shop for the summer sales. The assumed bu
A rectangular plate has two holes of dimensions shown and is released from the position shown. The plate is hinged about a horizontal axis and can rotate in the vertical plane. An
Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!
whatsapp: +91-977-207-8620
Phone: +91-977-207-8620
Email: [email protected]
All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd