Q. Design Pumps for plant layout?
Pumps handling flammable or combustible materials are relatively frequent sources of leakage and should therefore be located as far as practical from continuous ignition sources. They should not be located beneath other equipment, such as towers, drums, or pipe racks in order to avoid fire involvement of such equipment. Also, they should be located clear of overhead obstructions so they can be reached by a small crane. Where pumps are located within multi-level structures and portable crane access is not possible, monorails shall be installed for removal of the pump or internals during maintenance. A preferred location for pumps is on the opposite side of towers, away from fired heaters. In-line pumps should be treated the same as regular pumps for spacing purposes.
Hot pumps handling flammable materials present an increased fire risk because of the high likelihood of auto-ignition if a leak occurs. Pumps containing hydrocarbons operating above 316 °C (600 °F) or above its auto-ignition temperature (whichever is lower) should preferably not be located under or within multi-level structures. If unavoidable, fire protection measures such as passive fire protection or water sprays are required for equipment and structures above the pumps. However, the best choice is not to locate such pumps under or within structures.
Spacing separates pumps with higher fire potential and provides access for fire fighting. When a pump and its spare are exposed to a common fire hazard, additional separation between them may be justified to minimize the risk of losing both of them during a fire.
Pumps at grade should have prepared foundations with a paved area sloped to take spillage away from the pumps. Where pumps are required to be located in a structure, drip trays and anti-vibration mountings should be considered. For severe weather protection or noise reduction purposes some exposed pumps in critical service may be located in an enclosed or semi-enclosed shelter. In off-site areas, pumps should be grouped together outside the tank bermed areas.
Equilibrium conditions: What are equilibrium conditions for non concurrent force system? Sol.: For the Equilibrium of non concurrent forces there are three conditions:
Define Properties of System For defining any type of system particular parameters are required. Properties are those observable characteristics of the system, which can be util
Calculation for Stress-strain carves: After reaching point D, if bar is strained further, a local reduction in cross section occurs in gauge length (that is, formati
Problem: (a) What is the best paper to use when printing metallic inks? Explain your answer. (b) A multiple page printed document such as a book, brochure or booklet needs f
Q. Show the Sources of Ignition? Sources of Ignition - Possible sources of ignition include the following: • Electrical: Sparks or arcs may occur when current carrying cont
Fracture toughness of material of plate: A large thin plate carrying a crack of 70 mm at its centre is subjected to fluctuating stress cycle perpendicular to crack. s max = 7
what is structure with example
Evaluate the stream function at point (2, 3) for a two dimensional flow given by U = 5x 3 v = - 15x 2 y Evaluate the velocity potential function for a two dimension
Calculate stress intensity factor: For the plate in Figure (a) W = 25 mm, 2a = 10 mm, plate thickness, t = 2 mm, Load P = 1000 N. Calculate stress intensity factor if length o
#quesThe spring controlled governor of the “Hartung” type has two rotating masses each of 3.5 kg and the limits of their radius of rotation are 100 mm and 125 mm. The each mass is
Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!
whatsapp: +91-977-207-8620
Phone: +91-977-207-8620
Email: [email protected]
All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd