Q. Design Pumps for plant layout?
Pumps handling flammable or combustible materials are relatively frequent sources of leakage and should therefore be located as far as practical from continuous ignition sources. They should not be located beneath other equipment, such as towers, drums, or pipe racks in order to avoid fire involvement of such equipment. Also, they should be located clear of overhead obstructions so they can be reached by a small crane. Where pumps are located within multi-level structures and portable crane access is not possible, monorails shall be installed for removal of the pump or internals during maintenance. A preferred location for pumps is on the opposite side of towers, away from fired heaters. In-line pumps should be treated the same as regular pumps for spacing purposes.
Hot pumps handling flammable materials present an increased fire risk because of the high likelihood of auto-ignition if a leak occurs. Pumps containing hydrocarbons operating above 316 °C (600 °F) or above its auto-ignition temperature (whichever is lower) should preferably not be located under or within multi-level structures. If unavoidable, fire protection measures such as passive fire protection or water sprays are required for equipment and structures above the pumps. However, the best choice is not to locate such pumps under or within structures.
Spacing separates pumps with higher fire potential and provides access for fire fighting. When a pump and its spare are exposed to a common fire hazard, additional separation between them may be justified to minimize the risk of losing both of them during a fire.
Pumps at grade should have prepared foundations with a paved area sloped to take spillage away from the pumps. Where pumps are required to be located in a structure, drip trays and anti-vibration mountings should be considered. For severe weather protection or noise reduction purposes some exposed pumps in critical service may be located in an enclosed or semi-enclosed shelter. In off-site areas, pumps should be grouped together outside the tank bermed areas.
A steel member supported by a tie bar has a load of 15 000 lbs on it. If the force on the steel member of 1.2 in 2 cross section is 14,180 lbs and the force on the tie bar of diam
how to calculate flow rate of liquid nitrogen? melting point(-210deg) boiling point(-195.8deg) critical temp(-149.9deg) relative density(0.8) specific gravity(808.5kg/m^3) rel
General Resource Models In computer controlled scheduling, material, machine handling equipment, tooling and buffer space should be comprised. The explicit consid
Efficiency Test on Sand Blasting: After the study on sand blasting, the result was acceptable and the next step is planning to make order for new machine and searc
Cemented Carbide These are minute pieces along with cutting edges and mechanically jointed or brazed to tool shank. This Carbide tool tips are generated by process of powder m
The stepped bar in Fig Q6 is stretched along the vertical axis and the maximum upward displacement is found to be 0.008 m. The bar has cross-sectional areas of A 1 and A 2 ov
New Rule with Local One Step Ahead Prediction: WLS Rule Along with an observation to improve the performance measure of the system, a dynamic posteriori rule, the WLS that is
Technical Limitations of Extension of screw conveyor Technical Limitations: Breakdown of hinged joint at intermediate condition of link. ?Not proper extension of coaxi
do you help me with an assignment in machin dynamics which need a solid works program and CAD prototype
What do you known by Investment casting ? What are main materials used for building the investment pattern ?
Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!
whatsapp: +91-977-207-8620
Phone: +91-977-207-8620
Email: [email protected]
All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd