Compute the worst voltage regulation, Electrical Engineering

Assignment Help:

Q. The following data were obtained on a 25- kVA, 2400:240-V, 60-Hz, single-phase distribution transformer:

• Open-circuit test with meters on LV side: 240 V, 3.2 A, 165 W

• Short-circuit test with meters on HV side: 55 V, 10.4 A, 375 W

Compute the worst voltage regulation and the power factor at which it occurs, when the transformer is delivering rated output at rated secondary terminal voltage of 240 V. Sketch the corresponding phasor diagram.


Related Discussions:- Compute the worst voltage regulation

SINGLE-PHASE INDUCTION MOTORS MOTORS, HOW DOES SINGLE PHASE INDUCTION MOTOR...

HOW DOES SINGLE PHASE INDUCTION MOTORS DEVELOP A STARTING TORQUE ?

Microprocessors, Microprocessors: We have learnt 8085 family of microp...

Microprocessors: We have learnt 8085 family of microprocessors. Initially, we understand basic components of a computer, 8085 microprocessor architecture and assembly language

find the thevenin and norton equivalent circuits, The output port of the o...

The output port of the one-port is defined by terminals A and B. Given: R 1 = 10 k_, R 2 = 20 k_, R 3 = 10 k_, and R 4 = 10 k_ V 1 = 20 V and I1 = 0.8 mA a) Find the T

Starting methods for polyphase induction motors, Starting Methods for Polyp...

Starting Methods for Polyphase Induction Motors When high starting torques are required, a wound-rotor induction motor, with external resistances inserted in its rotor circuits

Determine the h-parameters for the network., Q. A negative impedance conver...

Q. A negative impedance converter circuit shown in Figure is used in some applications where inductors cannot be utilized or where negative resistance is beneficial. (a) Determi

Explain djnz instructions of intel 8051 microcontroller, Explain DJNZ instr...

Explain DJNZ instructions of intel 8051 microcontroller? a) DJNZ Rn, rel Decrement the content of the register Rn and jump if not zero. b) DJNZ direct, rel Decreme

Standards and labelling - features of energy conservation, Standards and La...

Standards and Labelling - Features of Energy Conservation Standards and Labelling (S & L) has been recognized as a key activity for improvement in energy efficiency. The S & L

Create a time diagram - conveyer, When the PLC is in the RUN mode it will s...

When the PLC is in the RUN mode it will switch ON the conveyer so it will run continuously. This project is divided into four outcomes: (a)    Detect block on entry, close

Compute the required value, Q. In an AM transmitter that transmits a total ...

Q. In an AM transmitter that transmits a total power of 1 kW, the unmodulated carrier power is 850 W. Compute the required value of (S i /N i )AM at a receiver, if (S 0 /N 0 )AM

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd