Compute the worst voltage regulation, Electrical Engineering

Assignment Help:

Q. The following data were obtained on a 25- kVA, 2400:240-V, 60-Hz, single-phase distribution transformer:

• Open-circuit test with meters on LV side: 240 V, 3.2 A, 165 W

• Short-circuit test with meters on HV side: 55 V, 10.4 A, 375 W

Compute the worst voltage regulation and the power factor at which it occurs, when the transformer is delivering rated output at rated secondary terminal voltage of 240 V. Sketch the corresponding phasor diagram.


Related Discussions:- Compute the worst voltage regulation

Communication, can I get matlab code for out of band radiation reduction of...

can I get matlab code for out of band radiation reduction ofdm system

Explain the importance of distributing frames, Q. Explain the Importance of...

Q. Explain the Importance of distributing frames? Basically four levels of cabling are used as displayed in Figure. At the subscriber end, drop wires are taken to a distributio

Accounting, I need the solutions for this assignment

I need the solutions for this assignment

Which realization requires the least number of gates, Q. Consider a 1-bit v...

Q. Consider a 1-bit version of the digital comparator shown in Figure. Note that the operation of this circuit is such that whichever output is 1 gives the desired magnitude compar

Evaluate reference voltage, Q. Consider the 4-bit R-2R ladder D/A converter...

Q. Consider the 4-bit R-2R ladder D/A converter with V ref =-10 V. Determine the analog output voltage when the binary input code is 1100. Also, find what reference voltage is to

Specific orientation programme, Specific orientation programme: at this st...

Specific orientation programme: at this stage, induction is conducted by the foreman. Induction is specific and requires skill on the part of the foreman. A new employee must be p

Calculate the rms value, The sinusoidal voltage source in the circuit shown...

The sinusoidal voltage source in the circuit shown in Fig. is developing an rms voltage of 2000 V. The 4 ? load in the circuit is absorbing four times as much average power as the

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd