Q. The following data were obtained on a 25- kVA, 2400:240-V, 60-Hz, single-phase distribution transformer:

• Open-circuit test with meters on LV side: 240 V, 3.2 A, 165 W

• Short-circuit test with meters on HV side: 55 V, 10.4 A, 375 W

Compute the worst voltage regulation and the power factor at which it occurs, when the transformer is delivering rated output at rated secondary terminal voltage of 240 V. Sketch the corresponding phasor diagram.


Related Discussions:- Compute the worst voltage regulation

Covalent bonding, Covalent Bonding Exhibited through the diamond la...

Covalent Bonding Exhibited through the diamond lattice semiconductors. Each atom enclosed by four nearest neighbors, each comprising four electrons in the outermost orbi

Give a brief description of differentiating circuits, Q. Give a brief descr...

Q. Give a brief description of differentiating circuits ?                Differentiation is a measure of the rate of change. A differentiating circuit produces an output voltag

Determine modulation index, Q. If the output signal fromanAMmodulator is gi...

Q. If the output signal fromanAMmodulator is given by u(t) = 5 cos 1800 πt + 20 cos 2000 πt + 5 cos 2200 πt , determine: (a) The modulating signal m(t) and carrier c(t). (b)

Substations, How to calculate Electrical losses by transformation

How to calculate Electrical losses by transformation

Discuss important properties and uses of ceramics, Discuss important proper...

Discuss important properties and uses of Ceramics. Ceramics - These are materials made by high temperature firing treatment of natural clay and specific inorganic matters. The

Dee, how do we construct wind turbines. procedures methods

how do we construct wind turbines. procedures methods

Develop the equation of motion, Aloudspeaker is a common electrochemical tr...

Aloudspeaker is a common electrochemical transducer in which vibration is caused by changes in the input current to a coil which, in turn, is coupled to a magnetic structure that c

Calculate the e.m.f. generated in armature of a d.c. machine, The armature ...

The armature of a d.c. machine has a resistance of 0.3 and is connected to a 200V supply. Calculate the e.m.f. generated when it is running (a) as a generator giving 80A (b) as a

Use of capacitor in technical loss reduction, Use of Capacitor in Technical...

Use of Capacitor in Technical Loss Reduction The use of capacitors to correct for poor power factor is a well-built and cost-effective means of reducing distribution system lo

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd