The single-phase, 50-kVA, 2400:240-V, 60-Hz, two-winding distribution transformer is connected as a step-up autotransformer, as shown in Figure. Assume that the 240-V winding is provided with sufficient insulation to withstand a voltage of 2640 V to ground.
(a) Find VH , VX, IH , IC, and IX corresponding to rated (full-load) conditions.
(b) Determine the kVA rating as an autotransformer, and find how much of that is the conducted kVA.
(c) Based on the data given for the two-winding transformer, compute the efficiency of the autotransformer corresponding to full load, 0.8 power factor lagging, and compare it with the efficiency calculated for the two-winding transforme.
Q. Show how a 16-to-1 multiplexer can be used to implement the logic function described by the following truth table.
Q. Explain Crystal Oscillator The frequency of a crystal-controlled oscillator is held constant to a high degree of accuracy by the use of a quartz crystal. The frequency depen
what is peak inverse voltage?
Program Counter (PC) It is a 16 bit register. It is a memory pointer. It stores the memory address of the next byte of the program to be executed. Memory address is of
Theft or Pilferage of Power by the Existing Customers Power theft through the existing consumers is the predominant cause of loss of revenue to the electrical utilities. Almos
Q. A 300-kVA transformer has a core loss of 1.5 kW and a full-load copper loss of 4.5 kW. (a) Calculate its efficiency corresponding to 25, 50, 75, 100, and 125% loads at unity
A 10 - hp, 250-V shunt motor has an armature circuit resistance of 0.5 and a ?eld resistance of 200 . At no load, rated voltage, and 1200 r/min, the armature current is 3 A. At
Q. Important function of common control subsystem? If a call is destined to a number in an exchange other than present one processing the digits, initial translator generates t
Power in Balanced Three-Phase Circuits The total power delivered by a three-phase source, or consumed by a three-phase load, is found simply by adding the power in each of the
applications of heterodyne wave analyzer
Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!
whatsapp: +1-415-670-9521
Phone: +1-415-670-9521
Email: [email protected]
All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd