Compatibility Condition:

Total strain in steel = Total strain in copper

i.e. 3 × 10-4 + 1.965 × 10-5 Ps  = 4.5 × 10-4 + 1.8421 × 10-5 Pc

Recognising that Pc = - Ps, and dividing both sides by 10-5, we get

30 + 1.965 Ps = 45 - 1.8421 Ps

or        Ps = 45 - 30/ (1.965 + 1.8421) = 3.94 kN

∴          Stress in steel = 3.94 × 1000/ (π/4) × 182  = 15.5 N/mm2

∴          Stress in copper = - 3.94 × 1000/ (π /4)(302 - 182) = - 8.71 N/mm2


Related Discussions:- Compatibility condition

What do you mean by manhole loss, Q. What do you mean by Manhole loss? ...

Q. What do you mean by Manhole loss? Manholes are provided in locations where there are changes in direction, size and gradient of gravity pipelines. Generally practice for str

Calculate the daily standard production rate of equipment, Calculate the Da...

Calculate the Daily Standard Production Rate of Equipment An excavator with a bucket capacity of 3-yd 3 has a standard operating cycle time of 40 seconds. The daily standard p

Concepts and definitions of thermodynamics, System A system (often cal...

System A system (often called a closed system) is any collectionof matter within a prescribed boundary, but no matter may enter or leave the system.  Note 1. That the bo

Edge piles take up more loads than central piles, Edge piles take up more l...

Edge piles take up more loads than central piles in rigid cap Because of the effect of interaction of individual piles, central piles tend to settle more than the edge piles w

Show the side clearance of pipes in trenches, Side clearance of pipes in tr...

Side clearance of pipes in trenches From the design point of view, it's predominant to minimize the width of pipe trenches due to thebelow reasons: (i)  Higher cost of exca

Explain detention or retention ponds - hydrology, Explain Detention or Rete...

Explain Detention or Retention Ponds Detention/Retention Ponds: Designed to reduce and contain the peak runoff from developed areas (more impervious). Attempt to limit the runo

Execution compression test for concrete, Question In execution compression...

Question In execution compression test for concrete , have to test cubes .Test cylinders be approved? Answer Essentially, results of compression test carried out by using cu

Estimation of design flood discharge, Q. Estimation of design flood dischar...

Q. Estimation of design flood discharge? These methods are also in vogue for estimating maximum discharge. Discharge estimated using the above three methods may be compared wit

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd