Calculate the surface dimensions of sedimentation tank, Civil Engineering

Assignment Help:

Calculate the surface dimensions of Sedimentation Tank

A treatment plant upgrade calls for design of sedimentation basins to handle a flow rate of 8 MGD. The basins are for a Type I suspension with an overflow rate (q0) of 650 gpd/ft2 a length to width ratio of 4:1, a weir overflow rate (qw) of 20,000 gpd/ft, The minimum settling zone depth is 10 ft and 1.5 ft is allowed for freeboard.

(a)  If 3 tanks are chosen, what are the surface dimensions of each tank?

(b)  What is the required weir length for each tank?

(c)  What is the detention time

(a) As = settling zone surface area, ft2 Q = flow rate = 8,000,000 gal/d

q0 = overflow rate =650 gpd/ft2

Surface area of settling tank As = Q/q0 = 8*106 / 650= 12307 ft2

As = L w and Given L = 4 w

Since 3 tanks are used, As per tank = 12307 / 3 = 4102 ft2 = LW= (4W)W = 4W2

 W=32f t L = 4W = 128 ft Thus, L = 128 ft and W = 32 ft

(b) Overflow weir length Lw = (Q/tan K)/qw

Lw = overflow weir length (ft)           

qw = weir overflow rate (gpd//ft)

Q/tank = flow rate per tank (gpd) = 8MGD/3 = 2.67 MGD

Lw = (Q/tan K)/qw = 2.67 * 106 gpd/ 20000 gpd/ft = 133.4 ft

(c) detention time = V/Q = [128*32*10 ft3] /2.67MGD

= 40960 ft3 / [2.67*106 gal/day* ft3 /7.48gal]

= 0.11475 days = 2.75 hours


Related Discussions:- Calculate the surface dimensions of sedimentation tank

Explain the createthread function used in the windows nt, Explain the Creat...

Explain the CreateThread Function used in the Windows NT CreateThread(security, size, MyThreadFunction, arg, flag,&tID ) The CreateThread function call is used to start an i

Define fixed instrumentation - sounding or sensing devices, Define Fixed in...

Define Fixed instrumentation - Sounding or Sensing Devices? It is possible to monitor local scour at pier or abutment using fixed instrumentation as an alternative to the sound

Mini projcts in diaster management.., any new innovative metods to protct b...

any new innovative metods to protct building from disater

Determine the interdependent phases of investigation, Determine the interde...

Determine the interdependent phases of investigation The following are the interdependent phases of investigation: i)  Stratigraphical survey, ii) Physical survey, and

Calculate the aisc lrfd strength criteria, Check if the given beam and load...

Check if the given beam and loading satisfy the AISC LRFD strength criteria. The beam section is a W 16*31 of A36 steel and it is laterally supported at the ends at the load points

Cycle, what is motor cycle. please explain.

what is motor cycle. please explain.

Correction for construction period, You are aware that construction of any ...

You are aware that construction of any type of structure takes sometime. Pressure due to the building will be applied gradually and not instantaneously. Excavation for the construc

Epoxy-coated bars vs galvanized bars, Bonding performance to concrete: Epox...

Bonding performance to concrete: Epoxy-coated bars vs. galvanized bars  Based on the findings of CEB Bulletin 211 the bonding of galvanized bars to concrete is lower in early

State the volume change from the plastic limit, The plastic limit and liqui...

The plastic limit and liquid limit of a soil are 33% and 45% respectively. The percentage volume change from the liquid limit to the dry state is 36% of the dry volume. Likewise, t

What is the thickness of the concrete seal needed, Design a Cylindrical Ope...

Design a Cylindrical Open Caisson to be sunk by 30 m of sand to support a load of 50 MN. The allowable bearing pressure is 1700 kN/m 2 . Test the feasibility of sinking the caisson

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd