An electrical contractor is preparing to place the duct bank concrete encasement for the high voltage feeders between manhole # 11 and # 12, total distance is 323-ft. The duct bank is 2-ft x 3-ft and holds nine 4.5-in Schedule 80 PVC conduits. The amount of concrete to be ordered is most nearly:
Solution:
Nominal 4-in Schedule 80 PVC pipe is 4.5-in O.D.
Total Volume = 2' x 3' x 323' = 1938-ft3 / 27-ft3/CY = 71.77-yd3
Total Deduct = 9 x (π ((4.5"/12")/ft)2)/4 x 323' = 321-ft3 / 27-ft3/CY = 11.89-yd3
Total Concrete = 71.77-yd3 - 11.89-yd3 = 59.88-yds3
Calculate the Horizontal Distance A surveyor's total station measured slope distance near station 3245+26.35 is recorded as 437.380-m with a zenith angle of 118º 48' 07" and a
STONE Stone is a 'naturally available building material' used from the early age of civilization. It is available in the form of rocks, which is cut to needed size and shape an
equilibrium free body digram
DEFINITION TYPE STEP OF CONSTRUCTION STEP OF SAFETY
staircase
distomat
Maintenance of bituminous roads
Reinforcement of concrete in contact with internal vibrators At the time of concreting, if internal vibrators are placed accidentally in contact with some of the reinforcemen
how to design a new airport
Critical Path - Activity on Node The project precedence table shown below provides the relationships and durations of all activities. Based on end-of-day calculations for start
Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!
whatsapp: +1-415-670-9521
Phone: +1-415-670-9521
Email: [email protected]
All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd