Q. A shunt generator gives full load output of 30 kW at a terminal voltage of 200V. The armature and field resistance are 0.05? and 50? resp.. The iron and friction losses are 1000 W. Calculate
(1) generated emf (2) copper losses (3) efficiency
Ans.
Given
V = 200 V, P = 30 × 103 W,Ra = 0.05 W, Rsh = 50 W
Pi+f = 1000 W
I = P/V = 30 × 103/200 = 150 Amp
Ish = V/Rsh = 200/50 = 4A
Ia = I +Ish = 150 + 4 = 154 Amp
(a) E = V + Ia Ra = 200 + 154 × 0.05 = 207.7 volt
(b) Copper losses = Ia2 Ra + Iash Rsh
= (154)2 × 0.05 + (4)2 × 50 = 1985.8w
(c) Efficiency ? = Output/ Output + Copper losses + iron losses + friction loss
= 30 × 103/30 × 103 + 1985.8 + 1000 = 90.95%
(a) Design a 6-bit R-2 R ladder D/A converter. (b) For V ref = 10 V, find the maximum output voltage. (c) Determine the output voltage increment. (d) If the output voltag
The Octal Butters 74LS244 It has two group of four buffer with no inverted tri state output , controlled by two active low enable lines (1G and 2G) as shown in figur
Q. An RL series circuit carries a current of 0.02 cos 5000t A. For R = 100 and L = 20 mH, find the impedance of the series combination and determine the voltage across the series
Characteristics of magnetic field / flux lines: i. Forming a closing loop ii. Did not crossed against each other iii. Has a certain direction iv. Repel among one anot
Analog-to-Digital (A/D) Converters An A/D converter converts analog input signals into digital output data in many areas such as process control, aircraft control, and telemetr
problems on combination clipper
Q. For the circuits shown in Figure, sketch the frequency response (magnitude and phase) of ¯V out / ¯V in .
Stakeholders - Legal Requirements for Distribution licensees There have to be consultations among several stakeholders such as the licensees, the governments, consumers, gener
A battery having of 12 cells are divided in three group which each group having of four cells in series. The three groups are joined in parallel. The emf of every cell is 1.5V and
Quality of Supply and Services - Power Distribution For effectual management and performance improvement it is essential to measure the several defined parameters of the proc
Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!
whatsapp: +91-977-207-8620
Phone: +91-977-207-8620
Email: [email protected]
All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd