Calculate distance between top and bottom chord of the truss, Civil Engineering

Assignment Help:

A W12x58 member, which comprises a vertical member in a truss span, is subjected to a factored axial compressive force of 163 kips.  The W12x58 section is oriented such that the strong axis is subjected to wind loading.  For a grade 50 specimen, what is the maximum permitted uniformly distributed wind loading on truss vertical member, assuming the distance between top and bottom chord of the truss is 12-ft.?

The section is subjected to a combined loading of axial force and strong axis bending.  Because the member is part of a truss, it is assumed to be pinned at both ends. 

The first thing to determine is what the ratio of applied axial force to allowable is, to determine which interaction equation to use.

We can determine the allowable axial force for a given K and L values.  The problem doesn't explicitly use the term unbraced length.  However, for a vertical member in a truss, it is sufficient to use the vertical distance between the top and bottom chords.  Thus, L = 12 ft.  The k value is set to 1.0.  Therefore, the K*L value is then 12-ft. *1.0 = 12-ft.  From Table 4-1, this results in an allowable axial capacity of 603 kips

φPn = 603 kips

Pr = 163 kips

Pr / φPn = 163 kips / 603 kips = 0.27 which is greater than 0.2.  Therefore the first equation governs the capacity.

Next, the maximum permitted moment and the capacity is estimated at 306 kip*ft.

φMux = 306 kip*ft

Now, the interaction equation can be solved.

163 kip / (603 kip) + 8*Mr / (9*306 kip*ft) = 1.0

Solving for Mr = 251.2 kip*ft.  From this, the required distributed loading can be determined from the equation:

Mmax = wL2 / 8.  Solving for w, we obtain:

W = Mmax * 8 / L2 = 251.2 kip*ft * 8 / (12-ft.)^2 = 13.9 kip / ft. 

 


Related Discussions:- Calculate distance between top and bottom chord of the truss

Inadequate pile founding level, Reasons of common occurrence of "inadequate...

Reasons of common occurrence of "inadequate pile founding level" in piles of piers The most severe load on piers usually is the horizontal load owing to berthing and mooring o

Define the limitations of shock transmission unit, Define the Limitations o...

Define the Limitations of shock transmission unit? STUs are not intended for energy/shock absorption. They simply transmit load from one part of the structure to another thus s

Solid mensuration, the two sides of a triangle are 17cm and 28 cm long, and...

the two sides of a triangle are 17cm and 28 cm long, and the length of the median drawn to the third side is equal to 19.5. find the distance from an endpoint of this median to the

Advantages of unbonded post-tensioning systems, Advantages of unbonded post...

Advantages of unbonded post-tensioning systems Similarly, some advantages of unbonded post-tensioning systems over bonded post-tensioning ones may be written as under :  (a)

Which type of pile cap transfers loads equally to piles, Q. Which type of p...

Q. Which type of pile cap transfers loads equally to piles, flexible pile cap orrigid pile cap? Loads from columns transferring to pile cap persuade tensile forces at the bott

What is rapid sand filter, Q. What is Rapid Sand Filter? A Rapid Sand F...

Q. What is Rapid Sand Filter? A Rapid Sand Filter is a water treatment plant that includes provision for pre treating the water by coagulation and sedimentation for settlement

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd